What's New at Precision Digital News from Precision Digital Rate/Totalizers, Fluidwell, NOVA Rate/Totalizers, Fluidwell, NOVA Precision Digital Pricelists Precision Digital Services Precision Digital Support Services Instrumentation Design & Sales JobsContact Precision Digital CorporationView Precision Digital Videos
Fluidwell F010 Flow Rate Indicator
   
   


FLUIDWELL PRESSURE INDICATORS

Overview Application Terminal Connections Wiring Diagrams

Hazardous Area Application Specifications Ordering Information Documentation


F153 - PRESSURE MONITOR


Features
  • Displays actual pressure and alarm values.
  • 4 alarm values can be entered: low-low, low, high and high-high pressure alarm.
  • Large 17mm (0.67") digits.
  • Selectable on-screen engineering units mbar, bar, PSI or no unit.
  • Operational temperature -30°C up to +80°C (-22°F up to 178°F).
  • Very compact design for panel mount, wall mount or field mount applications.
  • Rugged aluminum field mount enclosure IP67 / NEMA 4X.
  • Intrinsically Safe ATEX Certification II 1 GD EEx ia IIB/IIC T4 T100°C.
  • Explosion/flame proof ATEX Certification II 2 GD EEx d IIB T5.
  • Alarm and analog signal outputs.
  • Full Modbus communication RS232/485/TTL.
  • Loop or battery powered, 8 - 24V AC/DC or115 - 230V AC power supply.
  • Sensor supply 3.2 / 8.2 / 12 / 24V DC.

Signal Input - Pressure

  • (0)4 - 20mA.
  • 0 - 10V DC.


Applications

For applications where continous pressure measurement and monitoring is important. Also re-transmission of the actual pressure or serial communication is required. Alternative basic model: F050 - F053

Signal Output

  • Up to 4 free configurable alarm outputs.
  • (0)4 - 20mA / 0 - 10V DC according to the pressure.

OVERVIEW


Introduction

The F153 is a versatile pressure indicator with continous pressure monitoring feature. It offers the facility to set two low pressure and two high pressure alarm values. If desired, an ignore function can be set up to allow for an incorrect pressure for a certain period of time. Up to four outputs are available to transmit the alarm condition. A wide selection of options further enhance this models capabilities, including Intrinsic Safety and full Modbus communication.

Display

The display has large 17mm (0.67”) and 8mm (0.31”) digits which displays the pressure, measuring unit and alarm values. The alarm values can be password protected. On-screen engineering units are easily configured from a comprehensive selection.

Configuration

All configuration settings are accessed via a simple operator menu which can be pass-code protected. Each setting is clearly indicated with an alphanumerical description, therefore avoiding confusing abbreviations. All settings are safely stored in EEPROM memory in the event of sudden power failure.

Analog Output Signal

The actual pressure is re-transmitted with the (0)4 - 20mA or 0 - 10V DC output signal. The output signal is updated ten times per second with a filter function being available to smoothen out the signal if desired. The output value is user defined in relation to the pressure, e.g. 4mA equals to 10 bar and 20mA equals to 100 bar. The output signal can be passive, active or isolated where the passive output type will loop power the F153 as well.

Alarm Output

Up to four configurable outputs are available to transmit the alarm condition. You can have e.g. two the same low alarm outputs, one high alarm output and one "all alarms" output. Type OS offers four mechanical relay outputs. However, only two outputs are available in Intrinsically Safe aplications. Three outputs are available in all other configurations. The output signals can be a passive NPN, active PNP or an isolated electro-mechanical relay.

Signal Input

The F153 accepts (0)4 - 20mA and 0 - 10V DC input signals from any type of pressure measurement device.

Communication

All process data and settings can be read and modified manually or through the Modbus communication link (RS232 / RS485). Full Modbus functionality remains available for the Intrinsically Safe version (TTL).

Hazardous area

For hazardous area applications, this model has been ATEX certified Intrinsically Safe ATEX Certification II 1 GD EEx ia IIB / IIC T4 T100°C with an allowed operational temperature of -30°C to +70°C (-22°F to +158°F). A flame proof enclosure is also available with the rating ATEX Certification II 2 GD EEx d IIB T5.

Enclosures

Various types of enclosures can be selected, all ATEX approved. As standard the F153 is supplied in a GRP panel mount enclosure, which can be converted to an IP67 / NEMA 4X GRP field mount enclosure by the addition of a back case. Most popular is our rugged aluminum field mount enclosure with IP67 / NEMA 4X rating. Both European or U.S. cable gland entry threads are available.

APPLICATION OVERVIEW


F153 Application Overview

ENCLOSURE


Aluminum & GRP Mount Enclosure


Loop-Powered General Purpose Indicator Enclosures

Aluminum Field/Wall Mount Enclosures

Loop-powered General indicator Fluidwell F090 Enclosures

Fluidwell HA Enclosure
HA
Fluidwell HM Enclosure
HM
Fluidwell HN Enclosure
HN
Fluidwell HO Enclosure
HO
Fluidwell HP Enclosure
HP
Fluidwell HT Enclosure
HT
Fluidwell HU Enclosure
HU
Fluidwell HU Enclosure
HV
Fluidwellr HZ Enclosure
HZ

GRP Field/Wall Mount Enclosures

Fluidwell HD Enclosure
HD
Fluidwell HE Enclosure
HE
Fluidwell HF Enclosure
HF
Fluidwell HG Enclosure
HG
Fluidwell HH Enclosure
HH
Fluidwell HJ Enclosure
HJ
Fluidwell HK Enclosure
HK

TERMINAL CONNECTIONS

Terminal Connections

WIRING DIAGRAMS

Wiring Diagram F153-A-AP-CH-OT-PX

F010: Typical wiring diagram F010-P-PB-(PX)-(ZB)

Wiring Diagram F153-A-AA-CB-OA-PD

F010: Typical wiring diagram F010-A-PL-ZB

*Supply voltage: 3.2 / 8.2 / 12 / 24V DC to sensor

Wiring Diagram F153-A-AI-CI-OR-PM

F010: Typical wiring diagram F010-A-PX-ZB

*Supply voltage: 3.2 / 8.2 / 12 / 24V DC to sensor

Wiring Diagram F153-A-AP-CB-OS-PD

F010: Typical wiring diagram F010-P-PD-ZB

Supply voltage: 3.2 / 8.2 / 12 / 24V DC to sensor

HAZARDOUS AREA APPLICATIONS

The F153-XI has been ATEX approved by KEMA for use in Intrinsically Safe applications. It is approved according to ATEX Certification II 1 GD EEx ia IIB/IIC T4 T100°C for gas and dust applications with an operational temperature range of -30°C to +70°C (-22°F to +158°F). Besides the I.S. power supplies for the two alarm outputs, it is allowed to connect up to three I.S. power supplies in IIB applications or one in IIC applications. Full functionality of the F153 remains available, including two alarm outputs and 4 - 20mA output and Modbus communication (type CT). Power supply type PD-XI offers a sensor supply according to the connected power supply voltage at terminal 1. A flame proof enclosure with rating ATEX ATEX Certification II 2 GD EEx d IIB T5 is available as well.


Configuration example IIB
F153-A-AF-CT-OT-PL-XI - Input loop powered unit

F010: Configuration example

Configuration example IIB
F153-A-AP-CT-OT-PX-XI - Output loop powered

F010: Configuration example IIA - IIB and IIC - F010-P-PX-XI-(ZB) - Basic power supply 8 - 30 VDC

Configuration example IIB and IIC
F153-A-AP-(CT)-OT-PD-XI - Power supply 16 - 30V DC

F010: Configuration example IIA - IIB and IIC - F010-P-PX-XI-(ZB) - Basic power supply 8 - 30 VDC

Configuration example IIB
F153-A-AF-CT-OT-PD-XI - Power supply 16 - 30V DC

F010: Configuration example IIA - IIB and IIC - F010-P-PX-XI-(ZB) - Basic power supply 8 - 30 VDC

SPECIFICATIONS

Display

Type: High intensity reflective numeric and alphanumeric LCD, UV-resistant.
Dimensions: 90 x 40mm (3.5" x 1.6").
Digits: Seven 17mm (0.67") and eleven 8mm (0.31") digits. Various symbols and measuring units.
Refresh Rate: User definable: 8 times/sec. - 30 secs - off.
Option ZB: Transflective LCD with green LED backlight. Good readings in full sunlight and darkness.
   Note: ZB Only available for safe area applications

Operating Temperature

Standard unit: -30°C to +80°C (-22°F to +178°F).
Intrinsically Safe: -30°C to +70°C (-22°F to +158°F).

Power Requirements

Type PB: Long life Lithium battery - life-time depends upon settings and configuration - up to 5 years.
Type PC: Intrinsically Safe long life lithium battery - life-time depends upon settings and configuration - up to 5 years.
Type PD: 8 - 24V AC / DC ± 10%. Power consumption max. 10 Watt. Intrinsically Safe: 16 - 30V DC; power consumption max. 0.75 Watt.
Type PF: 24 VAC / DC ± 10% Power consumption max. 15 Watt
Type PL: Input loop powered from sensor signal 4 - 20mA (type “A”) - requires types AI or AF and OT.
Type PM: 115 - 230 VAC ± 10%. Power consumption max. 15 Watt
Type PX: 8 - 30V DC. Power consumption max. 0.5 Watt.
Type ZB: 12 - 24V DC ± 10% or type PD / PF / PM. Power consumption max. 1 Watt.
   Note: PB/PF/PM Not available Intrinsically Safe.
   Note: PF/PM The total consumption of the sensors and outputs may not exceed 400mA @ 24V.
   Note: For Intrinsically Safe applications, consult the safety values in the certificate.

Sensor Excitation

Type PB/PC/PX: 3.2V DC
   Note: This is not a real sensor supply. Only suitable for sensors with a very low power consumption.
Type PD: 3.2 / 8.2 / 12 / 24V DC - max. 50mA @ 24V DC.
Type PD-XI: The sensor supply voltage will be according to power supply as connected to terminal 1.
Type PF / PM: 3.2 / 8.2 / 12 / 24V DC - max. 400mA @ 24V DC.

Terminal Connections

Type: Removable plug-in terminal strip. Wire max. 1.5mm2 and 2.5mm2.

Data Protection

Type: EEPROM backup of all settings. Data retention at least 10 years
Pass-code: Configuration settings can be pass-code protected.

Environment

Electromagnetic compatibility: Compliant ref: EN 61326 (1997), EN 61010-1 (1993)

Hazardous Area

Intrinsically Safe Type XI: ATEX approval ref.: ATEX Certification II 1 GD EEx ia IIB/IIC T4 T100°C. Maximum ambient +70°C (158°F).
Explosion proof Type XF: ATEX approval ref.: ATEX Certification II 2 GD EEx d IIB T5. Dimensions of enclosure: 300 x 250 x 200mm (11.8" x 9.9" x 7.9") L x H x D.
  Weight: Appr. 15kg/33 lbs

Casing

Window: Polycarbonate window.
Sealing: Silicone.
Control keys: Three industrial micro-switch keys. UV-resistant silicone keypad.

Aluminum Wall / Field Mount Enclosures

General: Die-cast aluminum wall/field mount enclosure IP67 / NEMA 4X with 2-component UV-resistant coating.
  Dimensions: 130 x 120 x 75mm (5.12" x 4.72" x 2.95") - W x H x D.
  Weight: 1100 grams/2.42 lbs
Type HA: Cable entry: 2 x PG9 and 1 x M20.
Type HM: Cable entry: 2 x M16 and 1 x M20.
Type HN: Cable entry: 1 x M20.
Type HO: Cable entry: 2 x M20.
Type HP: Cable entry: 6 x M12.
Type HT: Cable entry: 1 x ½" NPT.
Type HU: Cable entry: 3 x ½" NPT.
Type HV: Cable entry: 4 x M20.
Type HZ: Cable entry: no holes.

GRP Wall / Field Mount Enclosures

General: GRP wall/field mount enclosure IP67 / NEMA 4X, UV-resistant and flame retardant.
  Dimensions: 130 x 120 x 75mm (5.12" x 4.72" x 2.95") - W x H x D.
  Weight: 600 grams/1.33 lbs
Type HD: Cable entry: no holes.
Type HE: Cable entry: 2 x Ø 16mm and 1 x Ø 20mm.
Type HF: Cable entry: 1 x Ø 22mm (7/8").
Type HG: Cable entry: 2 x Ø 20mm.
Type HH: Cable entry: 6 x Ø 12mm.
Type HJ: Cable entry: 3 x Ø 22mm (7/8").
Type HK: Flat bottom, cable entry: no holes.

Panel Mount Enclosures

Dimensions: 130 x 120 x 60mm (5.12" x 4.72" x 2.36") - W x H x D.
  Panel cut-out: 115 x 98mm (4.53" x 3.86") L x H.
Type HB: Die-cast aluminum panel mount enclosure IP65 / NEMA 4.
  Weight: 600 grams/1.33 lbs
Type HC: GRP panel mount enclosure IP65 / NEMA 4, UV-resistant and flame retardant.
  Weight: 450 grams/1 lb

ABS Wall / Field Mount Enclosures

General: Silicone free ABS wall/field mount enclosure IP65 with EPDM and PE sealings. UV-resistant polyester keypad (old HD enclosure).
  Dimensions: 130 x 114 x 71mm (5.1" x 4.5" x 2.8") - W x H x D.
  Weight: 450 grams/1 lb
Type HS: Cable entry: no holes.

Signal Input

Accuracy: Resolution: 14 bit. Error < 0.025mA / ± 0.125% FS. Low level cut-off programmable.
Update time: Four times per second.
  Span: 0.000010 - 999,999 with variable decimal position.
  Offset: -999,999 - 999,999
Type A: (0)4 - 20mA. Analog input signal can be scaled to any desired range within 0 - 20mA.
  Voltage drop: 2.5V @ 20mA.
Type U: 0 - 10V DC. Analog input signal can be scaled to any desired range within 0 - 10V DC.
  Load impedance: 3kΩ.
   Note For signal A and U: power supply to temperature sensor is required; e.g. PD

Analog Output

Function: Transmitting actual pressure.
Accuracy:10 bit. Error < 0.05%. Analog output signal can be scaled to any desired range.
Update time: Ten times per second.
Type AA: Active 4 - 20mA output (requires OA + PD, PF or PM).
Type AB: Active 0 - 20mA output (requires OA + PD, PF or PM).
Type AF: Passive floating 4 - 20mA output for Intrinsically Safe applications (requires XI + PC, PD or PL).
Type AI: Passive galvanically isolated 4 - 20mA output - also available for battery powered models (requires PB, PD, PF, PL or PM).
Type AP: Passive 4 - 20mA output - not isolated. Unit will be loop powered.
Type AU: Active 0 - 10V DC output (requires OA + PD, PF or PM).

Alarm Output

Function: User defined: low, low-low, high, high-high or all alarms output.
Type OA: Three active 24V DC transistor outputs (PNP); max. 50mA per output (requires AA + PD, PF or PM).
Type OR: Two electro-mechanical relay outputs isolated (N.O.) - max. switch power 230V AC - 0.5A (requires PF or PM) and one transistor output OT or OA (OA in combination with AA only).
Type OS: Four electro-mechanical relay outputs - isolated; max. switch power 230V AC - 0.5A per relay (requires AP and PD with 24V AC / DC).
Type OT:Three passive transistor outputs (NPN) - not isolated. Max. 50V DC - 300mA per output.
   Note: Intrinsically Safe applications: only two transistor outputs type OT available.

Communication Option

Function: Reading display information, reading / writing all configuration settings.
Protocol: Modbus ASCII / RTU
Speed: 1200 - 2400 - 4800 - 9600 baud.
Addressing: Maximum 255 addresses.
Type CB: RS232
Type CH: RS485 2-wire
Type CI: RS485 4-wire
Type CT: TTL Intrinsically Safe.

Operational

Displayed functions:
    • Actual Pressure
    • Low - low alarm value.
    • Low alarm value.
    • High alarm value
    • High - high alarm value.
    • Alarm values can be set (or only displayed).

Pressure

Digits: 6 digits.
Units: mbar, bar, PSI, no unit
Decimals: 0 - 1 - 2 - 3

Alarm Values

Digits: 7 digits.
Units: According to the settings for pressure
Decimals: According to the settings for pressure
Time units: According to the settings for pressure
Type of alarm: Low, high, low-low or high-high pressure alarm. Includes alarm delay time and configurable alarm outputs.

ACCESSORIES

Mounting Accessories

FWX-ACF02: Stainless steel wall mounting kit.
FWX-ACF05: Stainless steel pipe mounting kit (worm gear clamps not included).
FWX-ACF06: Two stainless steel worm gear clamps Ø 44 - 56mm.
FWX-ACF07: Two stainless steel worm gear clamps Ø 58 - 75mm.
FWX-ACF08: Two stainless steel worm gear clamps Ø 77 - 95mm.
FWX-ACF09: Two stainless steel worm gear clamps Ø 106 - 138mm.
FWX-ACF10: Customized Grevopal tag plates for ACF02 and ACF05, including stainless steel screws. Dimension: 95mm x 12.5mm (3.75” x 0.50”).

Cable Gland Accessories

FWX-ACF20: For HA enclosure, includes O-rings.
FWX-ACF25: For HE enclosure, includes locknuts and O-rings.
FWX-ACF26: For HF enclosure, includes locknuts and O-rings.
FWX-ACF27: For HG enclosure, includes locknuts and O-rings.
FWX-ACF28: For HH enclosure, includes locknuts and O-rings.
FWX-ACF29: For HJ enclosure, includes locknuts and O-rings.
FWX-ACF32: For HM enclosure, includes O-rings.
FWX-ACF33: For HN enclosure, includes O-rings.
FWX-ACF34: For HO enclosure, includes O-rings.
FWX-ACF35: For HP enclosure, includes O-rings.
FWX-ACF39: For HT enclosure, includes O-rings.
FWX-ACF40: For HU enclosure, includes O-rings.

Blind Plug Accessories

FWX-ACF50: For HA enclosure, includes O-rings.
FWX-ACF55: For HE enclosure, includes locknuts and O-rings.
FWX-ACF56: For HF enclosure, includes locknuts and O-rings.
FWX-ACF57: For HG enclosure, includes locknuts and O-rings.
FWX-ACF58: For HH enclosure, includes locknuts and O-rings.
FWX-ACF59: For HJ enclosure, includes locknuts and O-rings.
FWX-ACF62: For HM enclosure, includes O-rings.
FWX-ACF63: For HN enclosure, includes O-rings.
FWX-ACF64: For HO enclosure, includes O-rings.
FWX-ACF65: For HP enclosure, includes O-rings.
FWX-ACF69: For HT enclosure, includes O-rings.
FWX-ACF70: For HU enclosure, includes O-rings.

ORDERING INFORMATION

Standard Model Number Configuration: F153-A-AP-CX-EX-HC-IX-OT-PX-TX-XX-ZX

To aid in the construction of a Fluidwell model number a model configurator must be used. The path to this Configurator is contained in the link shown below. However, it would help to first review the options shown below.

NOTE: If you require the product to be Intrinsically Safe (ATEX, IECEx, CSA or c-us), the options you choose should only include those options that carry the ATEX symbol next to them. The Configurator will not allow you to mix and match options, unless the product is to be used in a Safe Area.

Once a new model is generated using the Configurator, you will
  1. see the price of the fully configured model
  2. have an opportunity to purchase the product
  3. have the capability to e-mail the configuration to us, yourself, or a third person

To launch the configurator, click here

Sensor Input Signal

A ATEX Certification (0)4 - 20mA input
U ATEX Certification 0 - 10 VDC input

Analog Output Signal

AA   Active 4 - 20mA output - requires OA + PD, PF or PM.
AB   Active 0 - 20mA output - requires OA + PD, PF or PM.
AF ATEX Certification I.S. floating 4 - 20mA output - requires XI + PC, PL or PD.
AI   Isolated 4 - 20mA output - requires PB, PD, PF, PL or PM
AP ATEX Certification Passive 4 - 20mA output, loop powered unit
AU   Active 0 - 10V DC output - requires OA + PD, PF or PM

Communication

CB   Communication RS232 - Modbus ASCII / RTU
CH   Communication RS485 - 2-wire - Modbus ASCII / RTU
CI   Communication RS485 - 4-wire - Modbus ASCII / RTU
CT ATEX Certification Intrinsically Safe TTL - Modbus ASCII / RTU
CX ATEX Certification No communication

Flow Equations

EX ATEX Certification No flow equations

Panel Mount Enclosures - IP65 / NEMA 4

HB ATEX Certification Aluminum enclosure
HC ATEX Certification GRP enclosure

GRP Field / Wall Mount Enclosures - IP67 / NEMA 4X

HD ATEX Certification Cable entry: no holes
HE ATEX Certification Cable entry: 2 x Ø 16mm & 1 x Ø 20mm
HF ATEX Certification Cable entry: 1 x Ø 22mm (7/8")
HG ATEX Certification Cable entry: 2 x Ø 20mm
HH ATEX Certification Cable entry: 6 x Ø 12mm
HJ ATEX Certification Cable entry: 3 x Ø 22mm (7/8")
HK ATEX Certification Flat bottom, cable entry: no holes

Aluminum Field / Wall Mount Enclosures - IP67 / NEMA 4X

HA ATEX Certification Cable entry: 2 x PG9 + 1 x M20
HM ATEX Certification Cable entry: 2 x M16 + 1 x M20
HN ATEX Certification Cable entry: 1 x M20
HO ATEX Certification Cable entry: 2 x M20
HP ATEX Certification Cable entry: 6 x M12
HT ATEX Certification Cable entry: 1 x ½" NPT
HU ATEX Certification Cable entry: 3 x ½" NPT
HV ATEX Certification Cable entry: 4 x M20
HZ ATEX Certification Cable entry: no holes

ABS field / Wall Mount Enclosures

HS ATEX Certification Silicone free ABS field enclosure IP65 – Cable entry: no holes (old HD enclosure)

Additional Inputs

IX ATEX Certification No additional input.

Outputs

OA   Three active transistor outputs - requires AA, AB or AU and PD, PF or PM.
OR   Two mechanical relay outputs + one OT or OA - requires PF or PM.
OS   Four mechanical relay outputs - requires AP and PD.
OT ATEX Certification Three passive transistor outputs - standard configuration.

Power Supply

PB   Lithium battery powered
PC ATEX Certification Lithium battery powered - Intrinsically Safe
PD ATEX Certification 8 - 24V AC/DC + sensor supply - with XI: 16 - 30V DC.
PF   24 VAC / DC + sensor supply
PL ATEX Certification Input loop powered from sensor signal type “A” - requires AI or AF and OT.
PM   115 - 230 VAC + sensor supply
PX ATEX Certification Basic power supply 8 - 30V DC (no real sensor supply). Unit requires external loop AP.

Temperature Input Signal

TX ATEX Certification No temperature input signal

Hazardous Area

XI ATEX Certification Intrinsically Safe, according ATEX.
XF   EExd enclosure - 3 keys
XX   Safe area only

Other Options

ZB ATEX Certification Backlight
ZX ATEX Certification No options

The bold marked text contains the standard configuration.

DOCUMENTATION

The documentation can be downloaded from these links:
F153: Data Sheet
Request an Instruction Manual
Fluidwell Information
Low-Cost Explosion Proof Enclosure
 

See How You can Use Precision Digital Products for
View Flow Level, Pressure and Temperature Applications
 What's New | News | Products | Pricelist | Services | Support | Jobs | Contact Us | Site Map
Precision Digital: Distributors and Manufacturers of Digital Panel Meters and Indicators
View Flow Applications for PDC Products View Level Applications for PDC Products View Pressure Applications for PDC Products View Temperature Applications for PDC Products PDC Footer
User defined: batch process one or two stage control - scaled pulse output according the running batch or according accumulated total (one stage only).