Fluidwell F136 - Batch Controller |
|
Features
- Large display shows preset value and running batch value simultaneously.
- The analog output value reflects the course of the batch process; fourteen different profiles can be selected.
- Self-learning overrun correction.
- Easy operation to enter a batch value and to control the process.
- Count-up and count-down function available.
- Ability to process all types of flowmeter signals.
- Operational temperature -30 up to 80°C (-22 up to 178°F).
- Very compact design for panel mount, wall mount or field mount applications.
- Rugged aluminum field mount enclosure IP67/NEMA 4X.
- Intrinsically Safe
II 1 GD EEx ia IIB/IIC T4 T100°C.
- Explosion/flame proof
II 2 GD EEx d IIB T5.
- Full Modbus communication RS232/485/TTL.
- Loop or battery powered, 8 - 24V AC/DC or 115 - 230V AC power supply.
- Sensor supply 3.2 / 8.2 / 12 / 24V DC.
Signal Input - Flow
- Reed-switch.
- NAMUR.
- NPN/PNP pulse.
- Sine wave (coil).
- Active pulse signals.
- (0)4-20mA.
- 0 - 10V DC.
Signal Input - Status
- Remote control: start.
- Remote control: pause / stop.
|
Applications
For batch applications where retransmission of the course of the process is required. Alternative basic model: F030, F130 and F131
Signal Output
- Two configurable control outputs: for two-stage or one-stage control.
- (0)4-20mA / 0 - 10V DC according to the batch process.
- Scaled pulse output according to accumulated total.
|
|
OVERVIEW
Introduction
The F136 offers in addition to the standard functions an analog output signal in relation to the batch process. This to transmit the course of the process. The operator can enter a batch quantity easily or execute repeating batches. During the batch, the preset value is displayed as well as the batched (or remaining) quantity. The automatic self-learning overrun correction will ensure an accurate result each batch again.
Display
The display has large 17mm (0.67”) and 8mm (0.31”) digits. Besides the process information, a seven digit resettable "day total" is available as well as an eleven digit non-resettable accumulated total. All are backed-up in EEPROM memory every minute.
Configuration
All configuration settings are accessed via a simple operator menu which can be pass-code protected. Each setting is clearly indicated with an alphanumerical description, therefore avoiding confusing abbreviations and baffling codes. All settings are safely stored in EEPROM memory in the event of sudden power failure.
Analog Output Signal
The (0)4-20mA or 0 - 10V DC output signal is related to the batch process. For example, a 4mA will be generated when START has been pressed and this value will increase smoothly to 18.7mA when the overrun correction closes the valve. The end value will be 20mA when the batch is finished. Fourteen different profiles are available to re-transmit the course of the process (see section profiles). The output signal can be passive, active or isolated where the passive output type will loop power the F136 as well.
Control Output
Two outputs are available which can be configured to operate as two stage control for large batch quantities or one stage control for smaller batches, where the second output is available as a scaled pulse output. The output signals can be a passive NPN, active PNP or an isolated electro-mechanical relay.
Signal Input
The F136 will accept most pulse and analog input signals for flow or mass flow measurement. The input signal type can be selected by the user in the configuration menu without having to adjust any sensitive mechanical dip-switches or jumpers.
Communication
All process data and settings can be read and modified manually or through the Modbus communication link (RS232 / RS485). If desired, the batch process can even be started and stopped through communication. Full Modbus functionality remains available for the Intrinsically Safe version (TTL).
Hazardous area
For hazardous area applications, this model has been ATEX certified Intrinsically Safe II 1 GD EEx ia IIB / IIC T4 T100°C with an allowed operational temperature of -30°C to +70°C (-22°F to +158°F). A flame proof enclosure is also available with the rating II 2 GD EEx d IIB T5.
Enclosures
Various types of enclosures can be selected, all ATEX approved. As standard the F136 is supplied in a GRP panel mount enclosure, which can be converted to an field mount enclosure. Most popular is our rugged aluminum field mount enclosure with IP67 / NEMA 4X rating. Both European or U.S. cable gland entry threads are available.
APPLICATION OVERVIEW
ENCLOSURE
Aluminum & GRP Mount Enclosure
TERMINAL CONNECTIONS
WIRING DIAGRAMS
Wiring Diagram F136-P-AP-CH-OT-PX
*Supply voltage: 1.2 / 3.2V DC to sensor |
Wiring Diagram F136-A-AA-CB-OA-PD
*Supply voltage: 3.2 / 8.2 / 12 / 24V DC to sensor
|
Wiring Diagram F136-P-AP-CH-OR-PF
*Supply voltage: 1.2 - 3.2 - 8.2 - 12 - 24V DC to sensor
|
Wiring Diagram F136-A-AI-CI-OR-PM
*Supply voltage: 3.2 / 8.2 / 12 / 24V DC to sensor |
HAZARDOUS AREA APPLICATIONS
The F136-XI has been ATEX approved by KEMA for use in Intrinsically Safe applications. It is approved according to II 1 GD EEx ia IIB/IIC T4 T100°C for gas and dust applications with an operational temperature range of -30°C to +70°C (-22°F to +158°F). Besides the I.S. power supplies for the control outputs, it is allowed to connect up to three I.S. power supplies in IIB applications or one in IIC applications. Full functionality of the F136 remains available, including two stage control, 4-20mA output, pulse output and Modbus communication (type CT). Power supply type PD-XI offers a 8.2V sensor supply e.g. for one Namur sensor. A flame proof enclosure with rating ATEX II 2 GD EEx d IIB T5 is available as well.
Configuration example IIB and IIC F136-P-AP-(CT)-OT-PX-XI - Output loop-powered unit
Configuration example IIB F136-A-AF-CT-OT-(PC)-(PD)-(PL)-XI
Power supply 16 - 30V DC, battery or loop-powered
Profiles increasing output Selectable profiles analog output signal

|

|
 |
 |
 |
 |
 |
- -25%: Situation before a next batch start.
- 0%: The moment after START has been pressed.
- 75%: Valve will be closed due to the overrun correction.
- 100%: End of overrun-time which is end-of-batch.
- 125% Situation after end-of-batch.
|
Profiles decreasing output Selectable profiles analog output signal:

|

|
 |
 |
 |
 |
 |
- -25%: Situation before a next batch start.
- 0%: The moment after START has been pressed.
- 75%: Valve will be closed due to the overrun correction.
- 100%: End of overrun-time which is end-of-batch.
- 125% Situation after end-of-batch.
|
SPECIFICATIONS
Display
Type: High intensity reflective numeric and alphanumeric LCD, UV-resistant.
Dimensions: 90 x 40mm (3.5" x 1.6").
Digits: Seven 17mm (0.67") and eleven 8mm (0.31") digits. Various symbols and measuring units.
Refresh Rate: User definable: 8 times/sec. - 30 secs - off.
Option ZB: Transflective LCD with green LED backlight. Good readings in full sunlight and darkness.
Note: ZB Only available for safe area applications
Operating Temperature
Standard unit: -30°C to +80°C (-22°F to +178°F).
Intrinsically Safe: -30°C to +70°C (-22°F to +158°F).
Power Requirements
Type PB: Long life Lithium battery - life-time depends upon settings and configuration - up to 5 years.
Type PC: Intrinsically Safe long life lithium battery - life-time depends upon settings and configuration - up to 5 years.
Type PD: 8 - 24V AC / DC ± 10%. Power consumption max. 10 Watt. Intrinsically Safe: 16 - 30V DC; power consumption max. 0.75 Watt.
Type PF: 24 VAC / DC ± 10% Power consumption max. 15 Watt
Type PL: Input loop-powered from sensor signal 4-20mA (type “A”) - requires types AI or AF and OT.
Type PM: 115-230 VAC ± 10%. Power consumption max. 15 Watt
Type PX: 8 - 30V DC. Power consumption max. 0.5 Watt.
Type ZB: 12 - 24V DC ± 10% or type PD / PF / PM. Power consumption max. 1 Watt.
Note: PB/PF/PM Not available Intrinsically Safe.
Note: PF/PM The total consumption of the sensors and outputs may not exceed 400mA @ 24V.
Note: For Intrinsically Safe applications, consult the safety values in the certificate.
Sensor Excitation
Type PB/PC/PX: 3.2V DC for pulse signals and 1.2V DC for coil pick-up.
Note This is not a real sensor supply. Only suitable for sensors with a very low power consumption like coils (sine wave) and reed-switches.
Type PD: 1.2 / 3.2 / 8.2 / 12 / 24V DC - max. 50mA @ 24V DC.
Type PD-XI: 1.2 / 3.2 / 8.2V DC - max. 7mA @ 8.2V DC and mains power supply voltage (as connected to terminal 1).
Note: In case PD-XI and signal A or U: the sensor supply voltage is according to the power supply voltage connected to terminal 1. Also terminal 2 offers the same voltage.
Type PF / PM: 1.2 / 3.2 / 8.2 / 12 / 24V DC - max. 400mA @ 24V DC.
Terminal Connections
Type: Removable plug-in terminal strip. Wire max. 1.5mm2 and 2.5mm2.
Data Protection
Type: EEPROM backup of all settings. Backup of running totals every minute. Data retention at least 10 years
Pass-code: Configuration settings can be pass-code protected.
Environment
Electromagnetic compatibility: Compliant ref: EN 61326 (1997), EN 61010-1 (1993)
Hazardous Area
Intrinsically Safe Type XI: ATEX approval ref.: II 1 GD EEx ia IIB/IIC T4 T100°C. Maximum ambient +70°C (158°F).
Explosion-Proof Type XF: ATEX approval ref.: II 2 GD EEx d IIB T5. Dimensions of enclosure: 300 x 250 x 200mm (11.8" x 9.9" x 7.9") L x H x D.
Weight: Appr. 15kg/33 lbs
Casing
Window: Polycarbonate window.
Sealing: Silicone.
Control keys: Three industrial micro-switch keys. UV-resistant silicone keypad.
Panel Mount Enclosures
Dimensions: 130 x 120 x 60mm (5.12" x 4.72" x 2.36") - W x H x D.
Panel cut-out: 115 x 98mm (4.53" x 3.86") L x H.
Type HB: Die-cast aluminum panel mount enclosure IP65 / NEMA 4.
Weight: 600 grams/1.33 lbs
Type HC: GRP panel mount enclosure IP65 / NEMA 4, UV-resistant and flame retardant.
Weight: 450 grams/1 lb
Flowmeter Input
Type P: Coil / sine wave (minimum 20mVpp or 80mVpp - sensitivity selectable), NPN/PNP, open collector, reed switch, Namur, active pulse signals 8 - 12 and 24 VDC.
Frequency: Minimum 0Hz - maximum 7kHz for total and flow rate. Maximum frequency depends on signal type and internal low-pass filter. E.g. reed switch with low-pass filter: max. frequency 120Hz.
K-Factor: 0.000010 - 9,999,999 with variable decimal position
Low-pass Filter: Available for all pulse signals.
Option ZF: coil sensitivity 10mVpp.
Type A: (0)4-20mA. Analog input signal can be scaled to any desired range within 0 - 20mA.
Type U: 0 - 10 VDC. Analog input signal can be scaled to any desired range within 0 - 10 VDC.
Accuracy: Resolution:14 bit Error < 0.025mA / ± 0.125% FS. Low level cut-off programmable.
Span: 0.000010 - 9,999,999 with variable decimal position
Update time: Four times per second.
Voltage drop: Type A: max. 2.5 VDC @ 20mA.
Load impedance: Type U: 3kΩ.
Relationship: Linear and square root calculation.
Note: For signal type A and U: external power to sensor is required; e.g. type PD.
Logic Input
Function: Two terminal inputs to start, stop and reset the batch process.
Type: Internally pulled-up switch contact - NPN.
Duration: Minimum pulse duration 100msec.
Analog Outputs
Function: Transmitting process situation..
Accuracy: 10 bit. Error < 0.05%. Analog output signal can be scaled to any desired range.
Update time: Ten times per second.
Type AA: Active 4-20mA output (requires OA + PD, PF or PM).
Type AB: Active 0 - 20mA output (requires OA + PD, PF or PM).
Type AF: Passive floating 4-20mA output for Intrinsically Safe applications (requires XI + PC, PL or PD).
Type AI: Passive galvanically isolated 4-20mA output - also available for battery powered models (requires PB, PD, PF, PL or PM).
Type AP: Passive 4-20mA output - not isolated. Unit will be loop-powered.
Type AU: Active 0 - 10V DC output (requires OA + PD, PF or PM).
Control Output
Function: User defined: batch process one or two stage control - scaled pulse output according the running batch or according accumulated total.
Frequency: Max. 64Hz. Pulse length user definable between 7.8 msec up to 2 seconds.
Type OA: Two active 24V DC transistor outputs (PNP); max. 50mA per output (requires AA + PD, PF or PM).
Type OR: Two electro-mechanical relay outputs (N.O.) - isolated; max. switch power 230V AC - 0.5A per relay (requires PF or PM).
Type OT: Two passive transistor outputs (NPN) - not isolated. Max. 50V DC - 300mA per output.
Communication Option
Function: Reading display information, reading / writing all configuration settings.
Protocol: Modbus RTU.
Speed: 1200 - 2400 - 4800 - 9600 baud.
Addressing: Maximum 255 addresses.
Type CB: RS232
Type CH: RS485 2-wire
Type CI: RS485 4-wire
Type CT: TTL Intrinsically Safe.
Operational
Displayed functions:
• Preset value - can be entered by the operator.
• Batched quantity or remaining quantity.
• Total and accumulated total.
• Total can be reset to zero by pressing the STOP key twice.
Preset / Total
Digits: 7 digits.
Units: L, m3, GAL, USGAL, KG, lb, bbl, no unit
Decimals: 0 - 1 - 2 or 3.
Note: Total can be reset to zero.
Accumulated Total
Digits: 11 digits.
Units/Decimal: According to selection for total.
Note: Can not be reset to zero.
ORDERING INFORMATION
Standard Model Number Configuration: F136-P-AP-CX-EX-HC-IX-OT-PX-TX-XX-ZX
To aid in the construction of a Fluidwell model number a model configurator must be used. The path to this Configurator is contained in the link shown below. However, it would help to first review the options shown below.
NOTE: If you require the product to be Intrinsically Safe (ATEX, IECEx, CSA or c-us), the options you choose should only include those options that carry the ATEX symbol next to them. The Configurator will not allow you to mix and match options, unless the product is to be used in a Safe Area.
Once a new model is generated using the Configurator, you will
- see the price of the fully configured model
- have an opportunity to purchase the product
- have the capability to e-mail the configuration to us, yourself, or a third person
To launch the configurator, click here
Sensor Input Signal
| A |
 |
(0)4-20mA input |
| P |
 |
Pulse input: coil, npn, pnp, namur, reed-switch |
| U |
 |
0 - 10 VDC input |
Analog Output Signal
| AA |
|
Active 4-20mA output - requires OA + PD, PF or PM. |
| AB |
|
Active 0 - 20mA output - requires OA + PD, PF or PM. |
| AF |
 |
I.S. floating 4-20mA output - requires XI + PC, PL or PD. |
| AI |
|
Isolated 4-20mA output - requires PB, PD, PF, PL or PM |
| AP |
 |
Passive 4-20mA output, loop-powered unit |
| AU |
|
Active 0 - 10V DC output - requires OA + PD, PF or PM |
Communication
| CB |
|
Communication RS232 - Modbus RTU |
| CH |
|
Communication RS485 - 2-wire - Modbus RTU |
| CI |
|
Communication RS485 - 4-wire - Modbus RTU |
| CT |
 |
Intrinsically Safe TTL - Modbus RTU |
| CX |
 |
No communication |
Panel Mount Enclosures - IP65 / NEMA 4
| HB |
 |
Aluminum enclosure |
| HC |
 |
GRP enclosure |
Secondary Inputs
| IX |
 |
No additional input. |
Outputs
| OA |
|
One active transistor output - requires AA, AB or AU and PD, PF or PM. |
| OR |
|
One mechanical relay output - requires PF or PM |
| OT |
 |
One passive transistor output - standard configuration |
Power Supply
| PB |
|
Lithium battery powered |
| PC |
 |
Lithium battery powered - Intrinsically Safe |
| PD |
 |
8 - 24V AC/DC + sensor supply - with XI: 16 - 30V DC. |
| PF |
|
24 VAC / DC + sensor supply |
| PL |
 |
Input loop-powered from sensor signal type “A” - requires AI or AF and OT |
| PM |
|
115-230 VAC + sensor supply |
| PX |
 |
Basic power supply 8 - 30V DC (no real sensor supply). Unit requires external loop AP. |
Hazardous Area
| XI |
 |
Intrinsically Safe, according ATEX. |
| XF |
|
EExd enclosure - 3 keys |
| XX |
|
Safe area only |
Other Options
| ZB |
|
Backlight |
| ZF |
 |
Coil input 10mVpp |
| ZX |
 |
No options |
The bold marked text contains the standard configuration.
|