Features
- Large display shows preset value and running batch value simultaneously.
- Self-learning overrun correction.
- Easy operation to enter a batch value and to control the process.
- Count-up and count-down function available.
- Selectable on-screen engineering units; volumetric or mass.
- Ability to process all types of flowmeter signals.
- Operational temperature -30°C up to +80°C (-22°F up to 178°F).
- Very compact design for panel mount, wall mount or field mount applications.
- Rugged aluminum field mount enclosure IP67/NEMA 4X.
- Intrinsically Safe
II 1 GD EEx ia IIB/IIC T4 T100°C.
- Explosion/flame proof
II 2 GD EEx d IIB T5.
- Full Modbus communication RS232/485/TTL.
- Loop or battery powered, 8 - 24V AC/DC or 115 - 230V AC power supply.
- Sensor supply 3.2 / 8.2 / 12 / 24V DC.
- No-flow monitoring..
Signal Input - Flow
- Reed-switch.
- NAMUR.
- NPN/PNP pulse.
- Sine wave (coil).
- Active pulse signals.
- (0)4 - 20mA.
- 0 - 10V DC.
Status
- Remote control: start
- Remote control: pause / stop
|
|
Applications
For batching small up to very large quantities.
Single or repeating batches. Alternative basic
model: F030 or more sophisticated models:
F131 and F136
Signal Output
- Two configurable control outputs: for
two-stage or one-stage control.
- Scaled pulse output according to accumulated total (one stage control only).
|
|
OVERVIEW
Introduction
The F130 is a straight forward Batch controller offering exactly what is required for many applications. The operator can enter a batch quantity easily or execute repeating batches. During the batch, the preset value is displayed as well as the batched (or remaining) quantity and the units of measurement. The automatic self-learning overrun correction will ensure an accurate result each batch again. A wide selection of options further enhance this models capabilities, including Intrinsic Safety and full Modbus communication.
Display
The display has large 17mm (0.67”) and 8mm (0.31”) digits which are used to display the batched quantity and the preset value simultaneously. On-screen engineering units are easily configured from a comprehensive selection. A seven digit resettable "day total" is available as well as an eleven digit non-resettable accumulated total. All are backed-up in EEPROM memory every minute.
Configuration
All configuration settings are accessed via a simple operator menu which can be pass-code protected. Each setting is clearly indicated with an alphanumerical description, therefore avoiding confusing abbreviations and baffling codes. Once familiar with one F-series product, you will be able to program all models in the series without a manual. All settings are safely stored in EEPROM memory in the event of sudden power failure.
Control Output
Two outputs are available which can be configured to operate as two stage control for large batch quantities or one stage control for smaller batches. In this case, the second output is available as a scaled pulse output according to accumulated total or batch total. The pulse output length is user defined from 0.008 second up to 2 seconds. The maximum output frequency is 64Hz. The output signals can be a passive NPN, active PNP or isolated electro-mechanical relays.
Signal Input
The F130 will accept most pulse and analog input signals for flow or mass flow measurement. For remote control, two inputs are available to start, pause and stop the batch process.
No-Flow
If there is a predefined time-out in the input signal, the no-flow alarm will be triggered. The F130 goes in pause-mode and the display will show: NO FLOW.
Communication
All process data and settings can be read and modified manually or through the Modbus communication link (RS232 / RS485). If desired, the batch process can even be started and stopped through communication.
Hazardous area
For hazardous area applications, this model has been ATEX certified Intrinsically Safe II 1 GD EEx ia IIB / IIC T4 T100°C with an allowed operational temperature of -30°C to +70°C (-22°F to +158°F). A flame proof enclosure is also available with the rating II 2 GD EEx d IIB T5.
Enclosures
Various types of enclosures can be selected, all ATEX approved. The F130 is supplied in a GRP or rugged aluminum panel mount enclosure, which can be converted to an IP67 / NEMA 4X field mount enclosure. Both European or U.S. cable gland entry threads are available.
APPLICATION OVERVIEW
ENCLOSURE
Aluminum & GRP Mount Enclosure
Aluminum Field/Wall Mount Enclosures
 HA
|
 HM
|
 HN
|
 HO
|
 HP
|
 HT
|
 HU
|
 HV
|
 HZ
|
GRP Field/Wall Mount Enclosures
TERMINAL CONNECTIONS
WIRING DIAGRAMS
Wiring Diagram F130-P-CH-OT-PB-(PX)
*Supply voltage: 1.2 / 3.2V DC to sensor |
Wiring Diagram F130-P-CH-OT-PX
*Supply voltage: 1.2 / 3.2V DC to sensor |
Wiring Diagram F130-A-CB-OA-PD
*Supply voltage: 3.2 / 8.2 / 12 / 24V DC to sensor |
Wiring Diagram F130-A-CI-OR-PM
*Supply voltage: 3.2 / 8.2 / 12 / 24V DC to sensor |
HAZARDOUS AREA APPLICATIONS
The F130-XI has been ATEX approved by KEMA for use in Intrinsically Safe applications. It is approved according to II 1 GD EEx ia IIB/IIC T4 T100°C for gas and dust applications with an operational temperature range of -30°C to +70°C (-22°F to +158°F). Besides the I.S. power supplies for the control outputs, it is allowed to connect up to two I.S. power supplies in IIB applications or one in IIC applications. Full functionality of the F130 remains available, including two stage control, pulse output and Modbus communication (type CT). Power supply type PD-XI offers a 8.2V sensor supply e.g. for one Namur sensor. A flame proof enclosure with rating ATEX II 2 GD EEx d IIB T5 is available as well.
Configuration example IIB and IIC
F130-P-(CT)-OT-PC-(PX)-XI - Battery powered unit
Configuration example IIB and IIC
F130-P-(CT)-OT-PX-XI - Basic power supply 8 - 30V DC
Configuration example IIB and IIC
F130-A-(CT)-OT-PL-XI - Input loop powered
Configuration example IIB and IIC
F130-A-(CT)-OT-PD-XI - Power supply 16 - 30V DC
SPECIFICATIONS
Display
Type: High intensity reflective numeric and alphanumeric LCD, UV-resistant.
Dimensions: 90 x 40mm (3.5" x 1.6").
Digits: Seven 17mm (0.67") and eleven 8mm (0.31") digits. Various symbols and measuring units.
Refresh Rate: User definable: 8 times/sec. - 30 secs - off.
Option ZB: Transflective LCD with green LED backlight. Good readings in full sunlight and darkness.
Note: ZB Only available for safe area applications
Operating Temperature
Standard unit: -30°C to +80°C (-22°F to +178°F).
Intrinsically Safe: -30°C to +70°C (-22°F to +158°F).
Power Requirements
Type PB: Long life Lithium battery - life-time depends upon settings and configuration - up to 5 years.
Type PC: Intrinsically Safe long life lithium battery - life-time depends upon settings and configuration - up to 5 years.
Type PD: 8 - 24V AC / DC ± 10%. Power consumption max. 10
Watt. Intrinsically Safe: 16 - 30V DC; power
consumption max. 0.75 Watt.
Type PF: 24 VAC / DC ± 10% Power consumption max. 15 Watt
Type PL: Input loop powered from sensor signal 4 - 20mA
(type “A”) - requires types OT
Type PM: 115 - 230 VAC ± 10%. Power consumption max. 15 Watt
Type PX: 8 - 30V DC. Power consumption max. 0.5 Watt.
Type ZB: 12 - 24V DC ± 10% or type PD / PF / PM.
Power consumption max. 1 Watt.
Note: PB/PF/PM Not available Intrinsically Safe.
Note: PF/PM The total consumption of the sensors and outputs
may not exceed 400mA @ 24V.
Note: For Intrinsically Safe applications, consult the safety values in the certificate.
Sensor Excitation
Type PB/PC/PX: 3.2V DC for pulse signals and 1.2V DC for coil pick-up.
Note This is not a real sensor supply. Only suitable for sensors with a very low power consumption like coils (sine wave) and reed-switches.
Type PD: 1.2 / 3.2 / 8.2 / 12 / 24V DC - max. 50mA @ 24V DC.
Type PD-XI: 1.2 / 3.2 / 8.2V DC - max. 7mA @ 8.2V DC and mains power supply voltage (as connected to terminal 1).
Note: In case PD-XI and signal A or U: the sensor supply
voltage is according to the power supply voltage
connected to terminal 1. Also terminal 2 offers the
same voltage.
Type PF / PM: 1.2 / 3.2 / 8.2 / 12 / 24V DC - max. 400mA @ 24V DC.
Terminal Connections
Type: Removable plug-in terminal strip. Wire max. 1.5mm2 and 2.5mm2.
Data Protection
Type: EEPROM backup of all settings. Backup of running
totals every minute. Data retention at least 10 years
Pass-code: Configuration settings can be pass-code protected.
Environment
Electromagnetic compatibility: Compliant ref: EN 61326 (1997), EN 61010-1 (1993)
Hazardous Area
Intrinsically Safe Type XI: ATEX approval ref.: II 1 GD EEx ia IIB/IIC T4 T100°C. Maximum ambient +70°C (158°F).
Explosion proof Type XF: ATEX approval ref.: II 2 GD EEx d IIB T5. Dimensions of enclosure: 300 x 250 x 200mm (11.8" x 9.9" x 7.9") L x H x D.
Weight: Appr. 15kg/33 lbs
Casing
Window: Polycarbonate window.
Sealing: Silicone.
Control keys: Three industrial micro-switch keys. UV-resistant silicone keypad.
Aluminum Wall / Field Mount Enclosures
General: Die-cast aluminum wall/field mount enclosure IP67 / NEMA 4X with 2-component UV-resistant coating.
Dimensions: 130 x 120 x 75mm (5.12" x 4.72" x 2.95") - W x H x D.
Weight: 1100 grams/2.42 lbs
Type HA: Cable entry: 2 x PG9 and 1 x M20.
Type HM: Cable entry: 2 x M16 and 1 x M20.
Type HN: Cable entry: 1 x M20.
Type HO: Cable entry: 2 x M20.
Type HP: Cable entry: 6 x M12.
Type HT: Cable entry: 1 x ½" NPT.
Type HU: Cable entry: 3 x ½" NPT.
Type HV: Cable entry: 4 x M20.
Type HZ: Cable entry: no holes.
GRP Wall / Field Mount Enclosures
General: GRP wall/field mount enclosure IP67 / NEMA 4X, UV-resistant and flame retardant.
Dimensions: 130 x 120 x 75mm (5.12" x 4.72" x 2.95") - W x H x D.
Weight: 600 grams/1.33 lbs
Type HD: Cable entry: no holes.
Type HE: Cable entry: 2 x Ø 16mm and 1 x Ø 20mm.
Type HF: Cable entry: 1 x Ø 22mm (7/8").
Type HG: Cable entry: 2 x Ø 20mm.
Type HH: Cable entry: 6 x Ø 12mm.
Type HJ: Cable entry: 3 x Ø 22mm (7/8").
Type HK: Flat bottom, cable entry: no holes.
Panel Mount Enclosures
Dimensions: 130 x 120 x 60mm (5.12" x 4.72" x 2.36") - W x H x D.
Panel cut-out: 115 x 98mm (4.53" x 3.86") L x H.
Type HB: Die-cast aluminum panel mount enclosure IP65 / NEMA 4.
Weight: 600 grams/1.33 lbs
Type HC: GRP panel mount enclosure IP65 / NEMA 4, UV-resistant and flame retardant.
Weight: 450 grams/1 lb
ABS Wall / Field Mount Enclosures
General: Silicone free ABS wall/field mount enclosure IP65 with EPDM and PE sealings. UV-resistant polyester keypad (old HD enclosure).
Dimensions: 130 x 114 x 71mm (5.1" x 4.5" x 2.8") - W x H x D.
Weight: 450 grams/1 lb
Type HS: Cable entry: no holes.
Flowmeter Input
Type P: Coil / sine wave (minimum 20mVpp or 80mVpp - sensitivity selectable), NPN/PNP, open collector, reed switch, Namur, active pulse signals 8 - 12 and 24 VDC.
Frequency: Minimum 0Hz - maximum 7kHz for total and flow rate. Maximum frequency depends on signal type and internal low-pass filter. E.g. reed switch with low-pass filter: max. frequency 120Hz.
K-Factor: 0.000010 - 9,999,999 with variable decimal position
Low-pass Filter: Available for all pulse signals.
Option ZF: coil sensitivity 10mVpp.
Type A: (0)4 - 20mA. Analog input signal can be scaled to any desired range within 0 - 20mA.
Type U: 0 - 10 VDC. Analog input signal can be scaled to any desired range within 0 - 10 VDC.
Accuracy: Resolution:14 bit Error < 0.025mA / ± 0.125% FS. Low level cut-off programmable.
Span: 0.000010 - 9,999,999 with variable decimal position
Update time: Four times per second.
Voltage drop: Type A: max. 2.5 VDC @ 20mA.
Load impedance: Type U: 3kΩ.
Relationship: Linear and square root calculation.
Note: For signal type A and U: external power to sensor is required; e.g. type PD.
Logic Input
Function:Two terminal inputs to start, pause and stop the
batch process.
Type: Internally pulled-up switch contact - NPN.
Duration: Minimum pulse duration 100msec.
Control / Pulse Output
Function:User defined: batch process one or two stage control
- scaled pulse output according the running batch or
according accumulated total (one stage only).
Frequency: Max. 64Hz. Pulse length user definable between
7.8 msec up to 2 seconds.
Type OA: Two active 24V DC transistor outputs (PNP);
max. 50mA per output (requires PD, PF or PM)
Type OR: Two electro-mechanical relay outputs (N.O.) - isolated;
max. switch power 230V AC - 0.5A per relay
(requires PF or PM).
Type OT: Two passive transistor outputs (NPN) - not isolated.
Max. 50V DC - 300mA per output.
Communication Option
Function: Reading display information, reading / writing preset
value and all configuration settings. Start, pause and
stop batch process
Protocol: Modbus ASCII / RTU.
Speed: 1200 - 2400 - 4800 - 9600 baud.
Addressing: Maximum 255 addresses.
Type CB: RS232
Type CH: RS485 2-wire
Type CI: RS485 4-wire
Type CT: TTL Intrinsically Safe.
Operational
Displayed functions:
• Preset value - can be entered by the operator
• Batched quantity or remaining quantity.
• Total and accumulated total.
• Total can be reset to zero by pressing the STOP-key
twice.
• No-flow alarm.
Preset and Total
Digits: 7 digits.
Units: L, m3, GAL, USGAL, KG, lb, bbl, no unit
Decimals: 0 - 1 - 2 or 3.
Note: Total can be reset to zero.
Accumulated Total
Digits: 11 digits.
Units/Decimal: According to selection for total.
Note: Can not be reset to zero.
ACCESSORIES
Mounting Accessories
FWX-ACF02: Stainless steel wall mounting kit.
FWX-ACF05: Stainless steel pipe mounting kit (worm gear clamps not included).
FWX-ACF06: Two stainless steel worm gear clamps Ø 44 - 56mm.
FWX-ACF07: Two stainless steel worm gear clamps Ø 58 - 75mm.
FWX-ACF08: Two stainless steel worm gear clamps Ø 77 - 95mm.
FWX-ACF09: Two stainless steel worm gear clamps Ø 106 - 138mm.
FWX-ACF10: Customized Grevopal tag plates for ACF02 and ACF05, including stainless steel screws. Dimension: 95mm x 12.5mm (3.75” x 0.50”).
Cable Gland Accessories
FWX-ACF20: For HA enclosure, includes O-rings.
FWX-ACF25: For HE enclosure, includes locknuts and O-rings.
FWX-ACF26: For HF enclosure, includes locknuts and O-rings.
FWX-ACF27: For HG enclosure, includes locknuts and O-rings.
FWX-ACF28: For HH enclosure, includes locknuts and O-rings.
FWX-ACF29: For HJ enclosure, includes locknuts and O-rings.
FWX-ACF32: For HM enclosure, includes O-rings.
FWX-ACF33: For HN enclosure, includes O-rings.
FWX-ACF34: For HO enclosure, includes O-rings.
FWX-ACF35: For HP enclosure, includes O-rings.
FWX-ACF39: For HT enclosure, includes O-rings.
FWX-ACF40: For HU enclosure, includes O-rings.
Blind Plug Accessories
FWX-ACF50: For HA enclosure, includes O-rings.
FWX-ACF55: For HE enclosure, includes locknuts and O-rings.
FWX-ACF56: For HF enclosure, includes locknuts and O-rings.
FWX-ACF57: For HG enclosure, includes locknuts and O-rings.
FWX-ACF58: For HH enclosure, includes locknuts and O-rings.
FWX-ACF59: For HJ enclosure, includes locknuts and O-rings.
FWX-ACF62: For HM enclosure, includes O-rings.
FWX-ACF63: For HN enclosure, includes O-rings.
FWX-ACF64: For HO enclosure, includes O-rings.
FWX-ACF65: For HP enclosure, includes O-rings.
FWX-ACF69: For HT enclosure, includes O-rings.
FWX-ACF70: For HU enclosure, includes O-rings.
ORDERING INFORMATION
Standard Model Number Configuration: F130-P-AX-CX-EX-HC-IX-OT-PX-TX-XX-ZX
To aid in the construction of a Fluidwell model number a model configurator must be used. The path to this Configurator is contained in the link shown below. However, it would help to first review the options shown below.
NOTE: If you require the product to be Intrinsically Safe (ATEX, IECEx, CSA or c-us), the options you choose should only include those options that carry the ATEX symbol next to them. The Configurator will not allow you to mix and match options, unless the product is to be used in a Safe Area.
Once a new model is generated using the Configurator, you will
- see the price of the fully configured model
- have an opportunity to purchase the product
- have the capability to e-mail the configuration to us, yourself, or a third person
To launch the configurator, click here
Sensor Input Signal
| A |
 |
(0)4 - 20mA input |
| P |
 |
Pulse input: coil, npn, pnp, namur, reed-switch |
| U |
 |
0 - 10 VDC input |
Analog Output Signal
| AX |
 |
No analog output. |
Communication
| CB |
|
Communication RS232 - Modbus ASCII / RTU |
| CH |
|
Communication RS485 - 2-wire - Modbus ASCII / RTU |
| CI |
|
Communication RS485 - 4-wire - Modbus ASCII / RTU |
| CT |
 |
Intrinsically Safe TTL - Modbus ASCII / RTU |
| CX |
 |
No communication |
Flow Equations
| EX |
|
No flow equations |
Panel Mount Enclosures - IP65 / NEMA 4
| HB |
 |
Aluminum enclosure |
| HC |
 |
GRP enclosure |
GRP Field / Wall Mount Enclosures - IP67 / NEMA 4X
| HD |
 |
Cable entry: no holes |
| HE |
 |
Cable entry: 2 x Ø 16mm & 1 x Ø 20mm |
| HF |
 |
Cable entry: 1 x Ø 22mm (7/8") |
| HG |
 |
Cable entry: 2 x Ø 20mm |
| HH |
 |
Cable entry: 6 x Ø 12mm |
| HJ |
 |
Cable entry: 3 x Ø 22mm (7/8") |
| HK |
 |
Flat bottom, cable entry: no holes |
Aluminum Field / Wall Mount Enclosures - IP67 / NEMA 4X
| HA |
 |
Cable entry: 2 x PG9 + 1 x M20 |
| HM |
 |
Cable entry: 2 x M16 + 1 x M20 |
| HN |
 |
Cable entry: 1 x M20 |
| HO |
 |
Cable entry: 2 x M20 |
| HP |
 |
Cable entry: 6 x M12 |
| HT |
 |
Cable entry: 1 x ½" NPT |
| HU |
 |
Cable entry: 3 x ½" NPT |
| HV |
 |
Cable entry: 4 x M20 |
| HZ |
 |
Cable entry: no holes |
ABS field / Wall Mount Enclosures
| HS |
 |
Silicone free ABS field enclosure IP65 – Cable entry: no holes (old HD enclosure) |
Additional Inputs
| IX |
 |
No additional input. |
Outputs
| OA |
|
One active transistor output - requires PD, PF or PM |
| OR |
|
One mechanical relay output - requires PF or PM |
| OT |
 |
One passive transistor output - standard configuration |
Power Supply
| PB |
|
Lithium battery powered |
| PC |
 |
Lithium battery powered - Intrinsically Safe |
| PD |
 |
8 - 24V AC/DC + sensor supply - with XI: 16 - 30V DC. |
| PF |
|
24 VAC / DC + sensor supply |
| PL |
 |
Input loop powered from sensor signal type "A" |
| PM |
|
115 - 230 VAC + sensor supply |
| PX |
 |
Basic power supply 8 - 30 VDC (no real sensor supply) |
Temperature Input Signal
| TX |
 |
No temperature input signal |
Hazardous Area
| XI |
 |
Intrinsically Safe |
| XF |
|
EExd enclosure - 3 keys |
| XX |
|
Safe area only |
Other Options
| ZB |
|
Backlight |
| ZF |
 |
Coil input 10mVpp |
| ZX |
 |
No options |
The bold marked text contains the standard configuration.