Fluidwell F127 - Flow Computer |
|
Features
- Displays compensated consumption (flow rate), total and accumulated total.
- Supply line: displays temperature and compensated flow rate.
- Return line: displays temperature and compensated flow rate.
- 7 digit resettable total.
- 11 digit accumulated total.
- Analog signal output.
- Very compact design for panel mount, wall mount or field mount applications.
- Operational temperature -30 up to 80°C (-22 up to 178°F).
- Rugged aluminum field mount enclosure IP67/NEMA 4X.
- Intrinsically Safe
II 1 GD EEx ia IIB/IIC T4 T100°C.
- Explosion/flame proof
II 2 GD EEx d IIB T5.
- Full Modbus communication RS232/ 485/ TTL.
- Loop or battery powered, 8 - 24V AC/DC or 115 - 230V AC power supply.
- Sensor supply 3.2 / 8.2 / 12 / 24V DC.
Signal Input - Flow
- Reed-switch.
- NAMUR
- NPN/PNP pulse
- Sine wave (coil)
- Active pulse signals
Signal Input - Temperature
- PT100 - 2 or 3 wire
- (0)4-20mA
- 0 - 10V DC
|
Applications
fuel consumption calculation for diesel engines on board of ships or locomotives, generators or burners. Alternative basic model: F116.
Signal Output
- (0)4-20mA / 0 - 10V DC according to
compensated flow rate.
|
|
OVERVIEW
Introduction
The flow computer Model F127 has been developed to calculate corrected differential liquid volume at normal conditions for generic products. A typical application is the measurement of fuel consumption by engines for power generators, e.g. on board ships and locomotives. The usual difficulties encountered in such applications include: pulsating flows, very low consumption readings, vibration and high ambient temperatures. These are all well catered for in the design and operation of the F127. The corrected volumetric flow in each line is calculated using the thermal expansion coefficient algorithm stored in the flow computer. The reference temperature can be defined as desired, e.g. 15°C, 20°C or 60°F.
Display
The display has large 17mm (0.67”) and 8mm (0.31”) digits which can be set to show flow rate, total and temperature. On-screen engineering units are easily configured from a comprehensive selection. The accumulated total can register up to 11 digits and is backed-up in EEPROM memory every minute.
Configuration
All configuration settings are accessed via a simple operator menu which can be pass-code protected. Each setting is clearly indicated with an alphanumerical description, therefore avoiding confusing abbreviations and baffling codes. Once familiar with one F-series product, you will be able to program all models in the series without a manual. All settings are safely stored in EEPROM memory in the event of sudden power failure.
Analog Output Signal
The calculated consumption (flow rate) is re-transmitted with the (0)4-20mA or 0 - 10V DC output signal. The output signal is updated ten times per second with a filter function being available to smoothen out the signal if desired. The output value is user defined in relation to the flow rate, e.g. 4mA equals to 15L/Hr and 20mA equals to 2000L/Hr. The output signal can be passive, active or isolated where the passive output type will loop power the F127 as well.
Signal Input
The flow computer measures the uncorrected volumetric flow and temperature in both supply and return line. The F127 will accept most pulse input signals for flow. For the temperature measurement, 2 or 3 wire PT100 elements or sensors with a (0)4-20mA / 0 - 10V DC output signal can be used.
Communication
All process data and settings can be read and modified manually or through the Modbus communication link (RS232 / RS485). Full Modbus functionality remains available for the Intrinsically Safe version (TTL).
Hazardous area
For hazardous area applications, this model has been ATEX certified Intrinsically Safe II 1 GD EEx ia IIB / IIC T4 T100°C with an allowed operational temperature of -30°C to +70°C (-22°F to +158°F). A flame proof enclosure is also available with the rating II 2 GD EEx d IIB T5.
Enclosures
Various types of enclosures can be selected, all ATEX approved. As standard the F127 is supplied in a GRP panel mount enclosure, which can be converted to an IP67 / NEMA 4X GRP field mount enclosure by the addition of a back case. Most popular is our rugged aluminum field mount enclosure with IP67 / NEMA 4X rating. Both European or U.S. cable gland entry threads are available.
APPLICATION OVERVIEW
ENCLOSURE
Aluminum & GRP Mount Enclosure
TERMINAL CONNECTIONS
WIRING DIAGRAMS
Wiring Diagram F127-P-(AP)-CH-EL-PB-TP
*Supply voltage: 1.2 / 3.2V DC to sensor |
Wiring Diagram F127-P-AP-CH-EL-PX-TA
*Supply voltage: 1.2 / 3.2V DC to sensor |
Wiring Diagram F127-P-AI-CI-EL-PD-TA
*Supply voltage: 1.2 / 3.2 / 8.2 / 12 / 24V DC to sensor |
Wiring Diagram F127-P-AA-CB-EL-PM-TP
*Supply voltage: 1.2 / 3.2 / 8.2 / 12 / 24V DC to sensor |
HAZARDOUS AREA APPLICATIONS
The F127-XI has been ATEX approved by KEMA for use in Intrinsically Safe applications. It is approved according to II 1 GD EEx ia IIB/IIC T4 T100°C for gas and dust applications with an operational temperature range of -30°C to +70°C (-22°F to +158°F). It is allowed to connect up to six I.S. power supplies in IIB applications or one I.S. power supply in IIC applications. Full functionality of the F127 remains available, including 4-20mA output according to the flow rate and Modbus communication (type CT). Power supply type PD-XI offers a 8.2V sensor supply e.g. for two Namur sensors. A flame proof enclosure with rating ATEX II 2 GD EEx d IIB T5 is available as well.
Configuration example IIB and IIC F127-P-(AP)-(CT)-EL-TP-PC-XI - Battery powered unit
Configuration example IIB and IIC F127-P-AP-CT-EL-PX-TP-XI - Output loop-powered
Configuration example IIB and IIC F127-P-AF-CT-EL-PD-TA-XI - Power supply 16 - 30V DC
Configuration example IIB F127-P-AF-CT-EL-PD-TA-XI - Power supply 16 - 30V DC
SPECIFICATIONS
Display
Type: High intensity reflective numeric and alphanumeric LCD, UV-resistant.
Dimensions: 90 x 40mm (3.5" x 1.6").
Digits: Seven 17mm (0.67") and eleven 8mm (0.31") digits. Various symbols and measuring units.
Refresh Rate: User definable: 8 times/sec. - 30 secs - off.
Option ZB: Transflective LCD with green LED backlight. Good readings in full sunlight and darkness.
Note: ZB Only available for safe area applications
Operating Temperature
Standard unit: -30°C to +80°C (-22°F to +178°F).
Intrinsically Safe: -30°C to +70°C (-22°F to +158°F).
Power Requirements
Type PB: Long life Lithium battery - life-time depends upon settings and configuration - up to 5 years.
Type PC: Intrinsically Safe long life lithium battery - life-time depends upon settings and configuration - up to 5 years.
Type PD: 8 - 24V AC / DC ± 10%. Power consumption max. 10 watt. Intrinsically Safe: 16 - 30V DC; power consumption max. 0.75 Watt.
Type PF: 24 VAC / DC ± 10% Power consumption max. 15 Watt
Type PL: Input loop-powered from sensor signal 4-20mA (type “A”) - requires types AI or AF. and OT
Type PM: 115-230 VAC ± 10%. Power consumption max. 15 Watt
Type PX: 8 - 30V DC. Power consumption max. 0.5 Watt.
Type ZB: 12 - 24V DC ± 10% or type PD / PF / PM. Power consumption max. 1 Watt.
Note: PB/PF/PM Not available Intrinsically Safe.
Note: PF/PM The total consumption of the sensors and outputs may not exceed 400mA @ 24V.
Note: For Intrinsically Safe applications, consult the safety values in the certificate.
Note: PF and PM are only available with PT100 temperature sensors type TP.
Sensor Excitation
Type PB/PC/PX: 3.2V DC for pulse signals and 1.2V DC for coil pick-up.
Note This is not a real sensor supply. Only suitable for sensors with a very low power consumption like coils (sine wave) and reed-switches.
Type PD: 1.2 / 3.2 / 8.2 / 12 / 24V DC - max. 50mA @ 24V DC.
Type PD-XI: 1.2 / 3.2 / 8.2V DC - max. 7mA @ 8.2V DC and mains power supply voltage (as connected to terminal 1).
Type PM: 1.2 / 3.2 / 8.2 / 12 / 24V DC - max. 400mA @ 24V DC.
Terminal Connections
Type: Removable plug-in terminal strip. Wire max. 1.5mm2 and 2.5mm2.
Data Protection
Type: EEPROM backup of all settings. Backup of running totals every minute. Data retention at least 10 years
Pass-code: Configuration settings can be pass-code protected.
Environment
Electromagnetic compatibility: Compliant ref: EN 61326 (1997), EN 61010-1 (1993)
Hazardous Area
Intrinsically Safe Type XI: ATEX approval ref.: II 1 GD EEx ia IIB/IIC T4 T100°C. Maximum ambient +70°C (158°F).
Explosion-Proof Type XF: ATEX approval ref.: II 2 GD EEx d IIB T5. Dimensions of enclosure: 300 x 250 x 200mm (11.8" x 9.9" x 7.9") L x H x D.
Weight: Appr. 15kg/33 lbs
Casing
Window: Polycarbonate window.
Sealing: Silicone.
Control keys: Three industrial micro-switch keys. UV-resistant silicone keypad.
Panel Mount Enclosures
Dimensions: 130 x 120 x 60mm (5.12" x 4.72" x 2.36") - W x H x D.
Panel cut-out: 115 x 98mm (4.53" x 3.86") L x H.
Type HB: Die-cast aluminum panel mount enclosure IP65 / NEMA 4.
Weight: 600 grams/1.33 lbs
Type HC: GRP panel mount enclosure IP65 / NEMA 4, UV-resistant and flame retardant.
Weight: 450 grams/1 lb
Flowmeter Input
Type P: Coil / sine wave (minimum 20mVpp or 80mVpp - sensitivity selectable), NPN/PNP, open collector, reed switch, Namur, active pulse signals 8 - 12 and 24 VDC.
Frequency: Minimum 0Hz - maximum 7kHz for total and flow rate. Maximum frequency depends on signal type and internal low-pass filter. E.g. reed switch with low-pass filter: max. frequency 120Hz.
K-Factor: 0.000010 - 9,999,999 with variable decimal position
Low-pass Filter: Available for all pulse signals.
Option ZF: coil sensitivity 10mVpp.
Temperature
Accuracy: Resolution: 14 bit. Error < 0.025mA / ± 0.125% FS Low level cut-off programmable.
Update time: Four times per second.
Type TA: (0)4-20mA. Analog input signal can be scaled to any desired range within 0 - 20mA.
Span: 0.000010 - 9,999,999 with variable decimal position.
Offset: 0.00 - 99,999.99 K.
Voltage drop: 2.5V @ 20mA.
Type TP: 2 or 3 wire PT100.
Range: -100°C to +200°C (-148°F to 392°F). Accuracy: 0.1°C (0.18°F).
Option ZV: Range: -200°C to +800°C (-328°F to 1832°F). Accuracy 0.5°C (0.9°F).
Type TU: 0 - 10V DC. Analog input signal can be scaled to any desired range within 0 - 10V DC.
Span: 0.000010 - 9,999,999 with variable decimal position.
Offset: 0.00 - 99,999.99 K.
Load impedance: 3kΩ.
Note 1 TA / TU are not available for PF and PM.
Note 2 For signal TA and TU: power supply to temperature sensor is required; e.g. PD.
Analog Output
Function: Transmitting compensated differential flow rate.
Accuracy: 10 bit. Error < 0.05%. Analog output signal can be scaled to any desired range.
Update time: Ten times per second
Type AA: Active 4-20mA output (requires PD, PF or PM)
Type AB: Active 0 - 20mA output (requires PD, PF or PM)
Type AF: Passive floating 4-20mA output for Intrinsically Safe applications (requires XI + PC or PD)
Type AI: Passive galvanically isolated 4-20mA output - also available for battery powered models (requires PB, PD, PF or PM)
Type AP: Passive 4-20mA output - not isolated. Unit will be loop-powered
Type AU: Active 0 - 10V DC output (requires PD, PF or PM)
Communication Option
Function: Reading display information, reading / writing all configuration settings.
Protocol: Modbus RTU.
Speed: 1200 - 2400 - 4800 - 9600 baud.
Addressing: Maximum 255 addresses.
Type CB: RS232
Type CH: RS485 2-wire
Type CI: RS485 4-wire
Type CT: TTL Intrinsically Safe.
Operational
Displayed functions:
• Compensated differential flow rate (consumption).
• Compensated differential total and accumulated total.
• Supply line - Inlet temperature and compensated flow rate.
• Return line - Outlet temperature and compensated flow rate.
• Total can be reset to zero by pressing the CLEAR-key twice.
Total
Digits: 7 digits.
Units: L, m3, GAL, USGAL, KG, lb, bbl, no unit
Decimals: 0 - 1 - 2 or 3.
Note: Total can be reset to zero.
Accumulated Total
Digits: 11 digits.
Units/Decimal: According to selection for total.
Note: Can not be reset to zero.
Flow Rate
Digits: 7 digits.
Units: mL, L, m3, Gallons, KG, Ton, lb, bl, cf, RND, ft3, scf, Nm3, Nl, igal - no units.
Decimals: 0 - 1 - 2 or 3.
Time units: /sec - /min - /hr - /day.
Line Temperature
Digits: 6 digits.
Units: °C, °F or K
Decimals: 1
Flow Equation
Type EG: Corrected gas volume.
Formula: Qnormal = Q x (1 + α (Tnormal - T)) where α = thermal expansion coefficient.
Normal pressure: Default: 1.013 bar.
Normal temperature: Default: 273.15K (0°C / 32°F)
ORDERING INFORMATION
Standard Model Number Configuration: F127-P-AP-CX-EL-HC-IX-OX-PX-TA-XX-ZX
To aid in the construction of a Fluidwell model number a model configurator must be used. The path to this Configurator is contained in the link shown below. However, it would help to first review the options shown below.
NOTE: If you require the product to be Intrinsically Safe (ATEX, IECEx, CSA or c-us), the options you choose should only include those options that carry the ATEX symbol next to them. The Configurator will not allow you to mix and match options, unless the product is to be used in a Safe Area.
Once a new model is generated using the Configurator, you will
- see the price of the fully configured model
- have an opportunity to purchase the product
- have the capability to e-mail the configuration to us, yourself, or a third person
To launch the configurator, click here
Sensor Input Signal
| P |
 |
Pulse input: coil, npn, pnp, namur, reed-switch |
Analog Output Signal
| AA |
|
Active 4-20mA output - requires PD, PF or PM. |
| AB |
|
Active 0 - 20mA output - requires PD, PF or PM. |
| AF |
 |
I.S. floating 4-20mA output - requires XI + PC or PD. |
| AI |
|
Isolated 4-20mA output - requires PB, PD, PF or PM. |
| AP |
 |
Passive 4-20mA output, loop-powered unit |
| AU |
|
Active 0 - 10V DC output - requires PD, PF or PM. |
Communication
| CB |
|
Communication RS232 - Modbus RTU |
| CH |
|
Communication RS485 - 2-wire - Modbus RTU |
| CI |
|
Communication RS485 - 4-wire - Modbus RTU |
| CT |
 |
Intrinsically Safe TTL - Modbus RTU |
| CX |
 |
No communication |
Flow Equations
| EL |
 |
Corrected liquid volume |
Panel Mount Enclosures - IP65 / NEMA 4
| HB |
 |
Aluminum enclosure |
| HC |
 |
GRP enclosure |
Power Supply
| PB |
|
Lithium battery powered |
| PC |
 |
Lithium battery powered - Intrinsically Safe |
| PD |
 |
16-30 VDC + sensor supply |
| PF |
|
24V AC/DC + sensor supply - only available with TP. |
| PM |
|
115 - 230V AC + sensor supply - only available with TP. |
| PX |
 |
Basic power supply 8 - 30V DC (no real sensor supply). Unit requires external loop AP. |
Temperature Input Signal
| TA |
 |
(0)4-20mA input. |
| TP |
 |
PT100 input. |
| TU |
 |
0 - 10V DC input. |
Hazardous Area
| XI |
 |
Intrinsically Safe |
| XF |
|
EExd enclosure - 3 keys |
| XX |
|
Safe area only |
Other Options
| ZB |
 |
Backlight |
| ZF |
 |
Coil input 10mVpp |
| ZV |
 |
PRTD-range -200°C / +800°C. |
| ZX |
 |
No options |
The bold marked text contains the standard configuration.
|