Fluidwell F118 - Flow Rate Monitor with Linearization |
|
Features
- Displays instantaneous flow rate, total and accumulated total
- Two alarm values can be entered: low and high flow rate alarm
- Ten point linearization of the flow curve - with interpolation
- Selectable on-screen engineering units; volumetric or mass
- Auto backup of settings and running totals
- Operational temperature -30 up to 80°C(-22 up to 178°F)
- Very compact design for panel mount, wall mount or field mount applications
- Rugged aluminum field mount enclosure IP67/NEMA 4X
- Intrinsically Safe
II 1 GD EEx ia IIB/IIC T4 T100°C
- Explosion/flame proof
II 2 GD EEx d IIB T5
- Alarm, analog and pulse signal outputs
- Full Modbus communication RS232/485/TTL
- Loop or battery powered, 8 - 24V AC/DC or 115 - 230V AC power supply
- Sensor supply 3.2 / 8.2 / 12 / 24V DC.
Signal Input
- Reed-switch
- NAMUR
- NPN/PNP pulse
- Sine wave (coil)
- Active pulse signals
- (0)4-20mA
- 0 - 10V DC
|
Applications
Automated (production) processes where a minimum and / or a maximum dispensed quantity has to be monitored continuously.
Signal Output
- Up to three free configurable alarm outputs
- (0)4-20mA / 0 - 10V DC according to linearized flow rate
- Up to three pulse outputs according to linearized accumulated total
|
|
OVERVIEW
Introduction
The F118 provides very precise linearization of the flowmeters signal. In addition to the average K-Factor or Span, ten linearization points can be entered. The unit will interpolate between these points greatly enhancing accuracy in any flow range. Moreover, continuous flow rate monitoring feature is available with low and high flow rate alarm values. A wide selection of options further enhance this models capabilities.
Display
The display has large 17mm (0.67”) and 8mm (0.31”) digits which can be set to show flow rate, totals and alarm values. On-screen engineering units are easily configured from a comprehensive selection. The accumulated total can register up to 11 digits and is backed-up in EEPROM memory every minute.
Configuration
All configuration settings are accessed via a simple operator menu which can be pass-code protected. Each setting is clearly indicated with an alphanumerical description, therefore avoiding confusing abbreviations and baffling codes. Once familiar with one F-series product, you will be able to program all models in the series without a manual. All settings are safely stored in EEPROM memory in the event of sudden power failure.
Analog Output Signal
The linearized flow rate is re-transmitted with the (0)4-20mA or 0 - 10V DC output signal. The output signal is updated ten times per second. The output value is user defined, e.g. 4mA equals to 15L/Hr and 20mA equals to 2000L/Hr. The output signal can be passive, active or isolated where the passive output type will loop power the F118 as well.
Alarm Output
Up to three outputs are available to transmit the flow rate alarm condition and/or to generate a pulse in relation to total. All free configurable, in such a way that you can have e.g. one low alarm output, one high alarm output and one pulse output. A maximum of two outputs are available in Intrinsically Safe applications. The output signals can be a passive NPN, active PNP or an isolated electro-mechanical relay.
Pulse Output
The scalable pulse output, reflects the count on the accumulated display. The pulse length is user defined from 0.008 second up to 2 seconds. The maximum output frequency is 64Hz.
Signal Input
The F118 will accept most pulse and analog input signals for flow or mass flow measurement. The input signal type can be selected by the user in the configuration menu without having to adjust any sensitive mechanical dip-switches or jumpers.
Communication
All process data and settings can be read and modified manually or through the Modbus communication link (RS232 / RS485). Full Modbus functionality remains available for the Intrinsically Safe version (TTL).
Hazardous area
For hazardous area applications, this model has been ATEX certified Intrinsically Safe II 1 GD EEx ia IIB / IIC T4 T100°C with an allowed operational temperature of -30°C to +70°C (-22°F to +158°F). A flame proof enclosure is also available with the rating II 2 GD EEx d IIB T5.
Enclosures
Various types of enclosures can be selected, all ATEX approved. As standard the F118 is supplied in a GRP panel mount enclosure, which can be converted to a GRP field mount enclosure. Most popular is our rugged aluminum field mount enclosure with IP67 / NEMA 4X rating. Both European or U.S. cable gland entry threads are available.
APPLICATION OVERVIEW
ENCLOSURE
TERMINAL CONNECTIONS
WIRING DIAGRAMS
Wiring Diagram F118-P-(AP)-CH-(OT)-PB
*Supply voltage: 1.2 / 3.2V DC to sensor |
Wiring Diagram F118-P-AP-CH-OT-PX
*Supply voltage: 1.2 / 3.2V DC to sensor |
Wiring Diagram F118-A-AA-CB-OA-PD
*Supply voltage: 3.2 / 8.2 / 12 / 24V DC to sensor |
Wiring Diagram F118-A-AI-CI-OR-PM
*Supply voltage: 3.2 / 8.2 / 12 / 24V DC to sensor |
HAZARDOUS AREA APPLICATIONS
The F118-XI has been ATEX approved by KEMA for use in Intrinsically Safe applications. It is approved according to II 1 GD EEx ia IIB/IIC T4 T100°C for gas and dust applications with an operational temperature range of -30°C to +70°C (-22°F to +158°F). Besides the two I.S. power supplies for the pulse and alarm outputs, it is allowed to connect up to three I.S. power supplies in IIB applications or one in IIC applications. Full functionality of the F118 remains available, including 4-20mA output, pulse and alarm outputs and Modbus communication (type CT). Power supply type PD-XI offers a 8.2V sensor supply e.g. for one Namur sensor. A flame proof enclosure with rating ATEX II 2 GD EEx d IIB T5 is available as well.
Configuration example IIB and IIC
F118-P-(AP)-(CT)-(OT)-PC-XI - Battery powered unit
Configuration example IIB and IIC
F118-P-AP-(CT)-OT-PX-XI - Output loop-powered
Configuration example IIB
F118-A-AP-CT-OT-PD-XI - Power supply 16 - 30V DC
Configuration example IIB
F118-A-AF-CT-OT-(PC)-(PD)-(PL)-XI
Power supply 16 - 30V DC, battery or loop-powered
SPECIFICATIONS
Display
Type: High intensity reflective numeric and alphanumeric LCD, UV-resistant.
Dimensions: 90 x 40mm (3.5" x 1.6").
Digits: Seven 17mm (0.67") and eleven 8mm (0.31") digits. Various symbols and measuring units.
Refresh Rate: User definable: 8 times/sec. - 30 secs - off.
Option ZB: Transflective LCD with green LED backlight. Good readings in full sunlight and darkness.
Note: ZB Only available for safe area applications
Operating Temperature
Standard unit: -30°C to +80°C (-22°F to +178°F).
Intrinsically Safe: -30°C to +70°C (-22°F to +158°F).
Power Requirements
Type PB: Long life Lithium battery - life-time depends upon settings and configuration - up to 5 years.
Type PC: Intrinsically Safe long life lithium battery - life-time depends upon settings and configuration - up to 5 years.
Type PD: 8 - 24V AC / DC ± 10%. Power consumption max. 10 Watt. Intrinsically Safe: 16 - 30V DC; power consumption max. 0.75 Watt
Type PF: 24 VAC / DC ± 10%. Power consumption max. 15 Watt.
Type PL: Input loop-powered from sensor signal 4-20mA
(type “A”) - requires types AI or AF and OT.
Type PM: 115-230 VAC ± 10%. Power consumption max. 15 Watt.
Type PX: 8-30 VDC. Power consumption max. 0.5 Watt.
Type ZB: 12 - 24V DC ± 10% or type PD / PF / PM. Power consumption max. 1 Watt.
Note: PB/PF/PM Not available Intrinsically Safe.
Note: PF/PM The total consumption of the sensors and outputs may not exceed 400mA @ 24 VDC.
Note: For Intrinsically Safe applications, consult the safety values in the certificate.
Sensor Excitation
Type PB/PC/PX: 3.2V DC for pulse signals and 1.2V DC for coil pick-up.
Note This is not a real sensor supply. Only suitable for sensors with a very low power consumption like coils (sine wave) and
reed-switches
Type PD: 1.2 / 3.2 / 8.2 / 12 / 24V DC - max. 50mA @ 24V DC.
Type PD-XI: 1.2 / 3.2 / 8.2V DC - max. 7mA@8.2V DC and mains power supply voltage (as connected to terminal 1)
Note: In case PD-XI and signal A or U: the sensor supply voltage is according to the power supply voltage connected to
terminal 1. Also terminal 2 offers the same voltage.
Type PF / PM: 1.2 / 3.2 / 8.2 / 12 / 24V DC - max. 400mA @ 24V DC.
Terminal Connections
Type: Removable plug-in terminal strip. Wire max. 1.5mm2 and 2.5mm2.
Data Protection
Type: EEPROM backup of all settings. Backup of running
totals every minute. Data retention at least 10 years
Pass-code: Configuration settings can be pass-code protected.
Environment
Electromagnetic compatibility: Compliant ref: EN 61326 (1997), EN 61010-1 (1993)
Hazardous Area
Intrinsically Safe Type XI: ATEX approval ref.: II 1 GD EEx ia IIB/IIC T4 T100°C. Maximum ambient +70°C (158°F).
Explosion-Proof Type XF: ATEX approval ref.: II 2 GD EEx d IIB T5. Dimensions of enclosure: 300 x 250 x 200mm (11.8" x 9.9" x 7.9") L x H x D.
Weight: Appr. 15kg/33 lbs
Casing
Window: Polycarbonate window.
Sealing: Silicone.
Control keys: Three industrial micro-switch keys. UV-resistant silicone keypad.
Panel Mount Enclosures
Dimensions: 130 x 120 x 60mm (5.12"; x 4.72" x 2.36") - W x H x D.
Panel cut-out: 115 x 98mm (4.53" x 3.86") L x H.
Type HB: Die-cast aluminum panel mount enclosure IP65 / NEMA 4.
Weight: 600 grams/1.33 lbs
Type HC: GRP panel mount enclosure IP65 / NEMA 4, UV-resistant and flame retardant.
Weight: 450 grams/1 lb
Signal Input
Type P: Coil / sine wave (minimum 20mVpp or 80mVpp - sensitivity selectable), NPN/PNP, open collector, reed switch, Namur, active pulse signals 8 - 12 and 24 VDC.
Frequency: Minimum 0Hz - maximum 7kHz for total and flow rate. Maximum frequency depends on signal type and internal low-pass filter. E.g. reed switch with low-pass filter: max. frequency 120Hz.
K-Factor: 0.000010 - 9,999,999 with variable decimal position
Low-pass Filter: Available for all pulse signals.
Option ZF: coil sensitivity 10mVpp.
Type A: (0)4-20mA. Analog input signal can be scaled to any desired range within 0 - 20mA.
Type U: 0 - 10 VDC. Analog input signal can be scaled to any desired range within 0 - 10 VDC.
Accuracy: Resolution: 14 bit Error < 0.025mA / ± 0.125% FS. Low level cut-off programmable.
Span: 0.000010 - 9,999,999 with variable decimal position
Update time: Four times per second.
Voltage drop: Type A: max. 2.5 VDC @ 20mA.
Load impedance: Type U: 3kΩ.
Relationship: Linear and square root calculation.
Note: For signal type A and U: external power to sensor is required; e.g. type PD.
Analog Output
Function: Transmitting linearized flow rate.
Accuracy: 10 bit. Error < 0.05%. Analog output signal can be
scaled to any desired range.
Update time: Ten times per second
Type AA: Active 4-20mA output (requires OA + PD, PF or PM)
Type AB: Active 0 - 20mA output (requires OA + PD, PF or PM)
Type AF: Passive floating 4-20mA output for Intrinsically Safe applications (requires XI + PC, PL or PD)
Type AI: Passive galvanically isolated 4-20mA output - also available for battery powered models (requires PB, PD, PF, PL or PM)
Type AP: Passive 4-20mA output - not isolated. Unit will be loop-powered
Type AU: Active 0 - 10V DC output (requires OA + PD, PF or PM)
Alarm/Pulse Output
Function: All outputs are user defined: pulse output, low or
high alarm output or all alarm outputs.
Frequency: Max. 64Hz. Pulse length user definable between
7.8 msec up to 2 seconds.
Type OA: Three active 24V DC transistor outputs (PNP); max. 50mA per output (requires AA + PD, PF or PM).
Type OR: Two electro-mechanical relay outputs (N.O.) - isolated;
max. switch power 230V AC - 0.5A per relay
(requires PF or PM).
Type OT: Three passive transistor outputs (NPN) - not isolated. Max. 50V DC - 300mA per output.
Note: Intrinsically Safe applications: only two transistor
outputs type OT available.
Communication Option
Function: Reading display information, reading / writing all configuration settings.
Protocol: Modbus RTU.
Speed: 1200 - 2400 - 4800 - 9600 baud.
Addressing: Maximum 255 addresses.
Type CB: RS232
Type CH: RS485 2-wire
Type CI: RS485 4-wire
Type CT: TTL Intrinsically Safe.
Operational
Displayed functions:
• Linearized flow rate and / or total
• Linearized total and accumulated total
• Low flow rate alarm value
• High flow rate alarm value
• Total can be reset to zero by pressing the
CLEAR-key twice
• Alarm values can be set (or only displayed)
Total
Digits: 7 digits.
Units: L, m3, GAL, USGAL, KG, lb, bbl, no units.
Decimals: 0 - 1 - 2 or 3.
Note: Total can be reset to zero.
Accumulated total
Digits: 11
Units/Decimals: According to selection for total.
Note: Can not be reset to zero; not displayed during
process.
Flow Rate
Digits: 7 digits.
Units: mL, L, m3, Gallons, KG, Ton, lb, bl, cf, RND, ft3, scf, Nm3, Nl, igal - no units.
Decimals: 0 - 1 - 2 or 3.
Time units: /sec - /min - /hr - /day.
Alarm values
Digits: 7 digits.
Units: According to selection for flow rate
Decimals: According to selection for flow rate
Time units: According to selection for flow rate
Type of alarm: Low and high flow rate alarm
Includes alarm delay time and configurable alarm
outputs
ORDERING INFORMATION
Standard Model Number Configuration: F118-P-AP-CX-EX-HC-IX-OT-PX-TX-XX-ZX
To aid in the construction of a Fluidwell model number a model configurator must be used. The path to this Configurator is contained in the link shown below. However, it would help to first review the options shown below.
NOTE: If you require the product to be Intrinsically Safe (ATEX, IECEx, CSA or c-us), the options you choose should only include those options that carry the ATEX symbol next to them. The Configurator will not allow you to mix and match options, unless the product is to be used in a Safe Area.
Once a new model is generated using the Configurator, you will
- see the price of the fully configured model
- have an opportunity to purchase the product
- have the capability to e-mail the configuration to us, yourself, or a third person
To launch the configurator, click here
Sensor Input Signal
| A |
 |
(0)4-20mA input |
| P |
 |
Pulse input: coil, npn, pnp, namur, reed-switch |
| U |
 |
0 - 10 VDC input |
Analog Output Signal
| AA |
|
Active 4-20mA output - requires OA + PD, PF or PM |
| AB |
|
Active 0 - 20mA output - requires OA + PD, PF or PM |
| AF |
 |
I.S. floating 4-20mA output - requires XI + PC, PL or PD |
| AI |
|
Isolated 4-20mA output - requires PB, PD, PF, PL or PM |
| AP |
 |
Passive 4-20mA output, loop-powered unit |
| AU |
|
Active 0 - 10V DC output - requires OA + PD, PF or PM |
Communication
| CB |
|
Communication RS232 - Modbus ASCII / RTU |
| CH |
|
Communication RS485 - 2-wire - Modbus ASCII / RTU |
| CI |
|
Communication RS485 - 4-wire - Modbus ASCII / RTU |
| CT |
 |
Intrinsically Safe TTL - Modbus ASCII / RTU |
| CX |
 |
No communication |
Flow Equations
| EX |
|
No flow equations |
Panel Mount Enclosures - IP65 / NEMA 4
| HB |
 |
Aluminum enclosure |
| HC |
 |
GRP enclosure |
Additional inputs
| IX |
 |
No external input |
Outputs
| OA |
|
One active transistor output - requires AA, AB or AU and PD, PF or PM |
| OR |
|
One mechanical relay output - requires PF or PM |
| OT |
 |
One passive transistor output - standard configuration |
Power Supply
| PB |
|
Lithium battery powered |
| PC |
 |
Lithium battery powered - Intrinsically Safe |
| PD |
 |
16-30 VDC + sensor supply |
| PF |
|
24 VAC / DC + sensor supply |
| PL |
 |
Input loop-powered from sensor signal 4-20mA (type A) |
| PM |
|
115-230 VAC + sensor supply |
| PX |
 |
Basic power supply 8-30 VDC (no real sensor supply) |
Temperature Input Signal
| TX |
 |
No temperature input signal |
Hazardous Area
| XI |
 |
Intrinsically Safe |
| XF |
|
EExd enclosure - 3 keys |
| XX |
|
Safe area only |
Other Options
| ZB |
 |
Backlight |
| ZF |
 |
Coil input 10mVpp |
| ZX |
 |
No options |
The bold marked text contains the standard configuration.
|