What's New at Precision Digital News from Precision Digital Rate/Totalizers, Fluidwell, NOVA Rate/Totalizers, Fluidwell, NOVA Precision Digital Pricelists Precision Digital Services Precision Digital Support Services Instrumentation Design & Sales JobsContact Precision Digital CorporationView Precision Digital Videos
Fluidwell F010 Flow Rate Indicator
   
   


FLUIDWELL FLOW RATE TOTALIZER

Overview Application Terminal Connections Wiring Diagrams

Hazardous Area Application Specifications Ordering Information Documentation


F014 - FLOW RATE INDICATOR / TOTALIZER WITH PULSE SIGNAL OUTPUT


Features
  • Displays instantaneous flow rate, total and accumulated total
  • Eight point linearization of the flowcurve - with interpolation
  • Large 17mm (0.67") digit selection for flow rate or total
  • Ability to process all types of flowmeter signals
  • Auto backup of settings and running totals
  • Operational temperature -40°C up to +80°C (-40°F up to 178°F)
  • Very compact design for panel mount, wall mount or field mount applications
  • Rugged aluminum field mount enclosure IP67/NEMA 4X
  • Intrinsically Safe - ATEX, IECEx, FM and CSA approval for gas and dust applications.
  • Explosion/flame proof ATEX Certification II 2 GD EEx d IIB T5.
  • LED backlight option
  • Loop or battery powered, 8 - 24V AC/DC or 115 - 230V AC power supply
  • Sensor supply 3.2 / 8.2 / 12 / 24V DC

Signal Input

  • Reed-Switch
  • NAMUR
  • NPN/PNP pulse
  • Sine wave (coil)
  • Active pulse signals
  • (0)4-20mA
  • 0-10 VDC

Applications

Liquid flow measurement with mechanical flowmeters where a precise calculation over the full measurement range is required. Also re-transmission of the totalizer function is desired. Alternative more advanced models: F112 - F118.

Signal Input

  • Scaled pulse output according to linearized
    accumulated total.

OVERVIEW

Introduction

The F016 is a local indicator with linearization to display the actual flow rate, total and nonresettable accumulated total. In addition to the average K-Factor or Span, eight linearization points can be entered with their frequencies or values. The unit will interpolate between these points greatly enhancing accuracy in any flowrange. This linearization effects all display information as well as the pulse output. A wide selection of options further enhance this models capabilities, including Intrinsic Safety.

Display

The display has large 17mm (0.67:) and 8mm (0.31") digits which can be set to show flow rate and totals. On-screen engineering units are easily configured from a comprehensive selection. The accumulated total can register up to 11 digits and is backed-up in EEPROM memory every minute, just as the running total. A smart display update function achieves a readable display even at -40°C / -40°F.

Backlight

For those applications where readability during day and night is an issue, a bi-color backlight is available. The background color green or amber and the intensity can be adjusted from the keyboard. The display is a transflective type, which means that a high contrast reading is guaranteed in full sunlight as well as during the night. This backlight option is also available Intrinsically Safe.

Configuration

All configuration settings are accessed via a simple operator menu which can be pass-code protected. Each setting is clearly indicated with an alphanumerical description, therefore avoiding confusing abbreviations. Once familiar with one F-series product, you will be able to program all models in the series without a manual.

Pulse output

The scaleable pulse output reflects the count on the accumulated display. The pulse length is user defined from 0.001 second up to 10 seconds. The maximum output frequency is 500Hz. The output signal can be a passive NPN or an active PNP transistor, or an isolated electro-mechanical relay.

Signal Input

The F016 will accept most pulse and analog input signals for flow or mass flow measurement. The input signal type can be selected by the user in the configuration menu without having to adjust any sensitive mechanical dip-switches, jumpers or trimmers. The analog input version is even available as 4 - 20mA input loop powered display.

Hazardous Area

For hazardous area applications, this model has been ATEX, IECEx, FM and CSA certified Intrinsically Safe for gas and dust applications, with an allowed operational temperature of -40°C to +70°C (-40°F to +158°F). A flame proof enclosure with ATEX certification offers the rating ATEX Certification II 2 GD EExd IIB T5.

Enclosures

Various types of enclosures can be selected, all ATEX, IECEx, FM and CSA approved. As standard the F016 is supplied in an GRP panel mount enclosure. Most popular is our aluminum field mount enclosure with IP67 / NEMA 4X rating. Both European or U.S. cable gland entry threads are available.

APPLICATION OVERVIEW


F016 Application Overview

ENCLOSURE


Aluminum & GRP Mount Enclosure


Loop-Powered General Purpose Indicator Enclosures

Aluminum Field/Wall Mount Enclosures

Loop-powered General indicator Fluidwell F090 Enclosures

Fluidwell HA Enclosure
HA
Fluidwell HM Enclosure
HM
Fluidwell HN Enclosure
HN
Fluidwell HO Enclosure
HO
Fluidwell HP Enclosure
HP
Fluidwell HT Enclosure
HT
Fluidwell HU Enclosure
HU
Fluidwell HU Enclosure
HV
Fluidwellr HZ Enclosure
HZ

GRP Field/Wall Mount Enclosures

Fluidwell HD Enclosure
HD
Fluidwell HE Enclosure
HE
Fluidwell HF Enclosure
HF
Fluidwell HG Enclosure
HG
Fluidwell HH Enclosure
HH
Fluidwell HJ Enclosure
HJ
Fluidwell HK Enclosure
HK

TERMINAL CONNECTIONS

Power Supply PB/PC - PD - PL - PX Power supply PF - PM
Power Supply PB/PC - PD - PL - PX Power supply PF - PM

WIRING DIAGRAMS

Wiring Diagram F016-P-(OT)-PB-(PX)-(ZB)

Wiring Diagram F016-P-(OT)-PB-(PX)-(ZB)

* Sensor supply voltage for pulse flowmeter type P:
Terminal 3: 1.2 / 3.2V DC.
* Sensor supply voltage for analog flowmeter type A / U:
Terminal 3: not available

Wiring Diagram F016-A-OT-PX-ZB

Wiring Diagram F016-A-OT-PX-ZB

* Sensor supply voltage for pulse flowmeter type P:
Terminal 3: 1.2 / 3.2V DC.
* Sensor supply voltage for analog flowmeter type A / U:
Terminal 3: not available.


Wiring Diagram F016-A-(OT)-PL-ZB

Wiring Diagram F016-A-(OT)-PL-ZB

Sensor supply: sensor is externally powered.


Wiring Diagram F016-P-OT-PD-ZB

Wiring Diagram F016-P-OT-PD-ZB

* Sensor supply voltage for pulse flowmeter type P:
Terminal 3: 1.2 / 3.2V DC. Terminal 6 with type PD: 8.2V DC.
* Sensor supply voltage for analog flowmeter type A / U:
Terminal 3: not available.
Terminal 6 with type PD: voltage as connected to terminal 5 (internally linked).


Wiring Diagram F016-P-OA-PF-ZB

Wiring Diagram F016-P-OA-PF-ZB

* Sensor supply voltage for pulse flowmeter type P:
Terminal 7: 1.2 / 3.2 / 8.2 / 12 / 24V DC.
* Sensor supply voltage for analog flowmeter type A / U:
Terminal 7: 8.2 / 12 / 24V DC.


Wiring Diagram F016-A-OT-PF-ZB

Wiring Diagram F016-A-OT-PF-ZB

* Sensor supply voltage for pulse flowmeter type P:
Terminal 7: 1.2 / 3.2 / 8.2 / 12 / 24V DC.
* Sensor supply voltage for analog flowmeter type A / U:
Terminal 7: 8.2 / 12 / 24V DC.


Wiring Diagram F016-A-OA-PM-ZB

Wiring Diagram F016-A-OA-PM-ZB
* Sensor supply voltage for pulse flowmeter type P:
Terminal 7: 1.2 / 3.2 / 8.2 / 12 / 24V DC.
* Sensor supply voltage for analog flowmeter type A / U:
Terminal 7: 8.2 / 12 / 24V DC.


Wiring Diagram F016-P-OR-PM-ZB

Wiring Diagram F016-P-OR-PM-ZB

* Sensor supply voltage for pulse flowmeter type P:
Terminal 7: 1.2 / 3.2 / 8.2 / 12 / 24V DC.
* Sensor supply voltage for analog flowmeter type A / U:
Terminal 7: 8.2 / 12 / 24V DC.

HAZARDOUS AREA APPLICATIONS


The F016-XI has been certified according ATEX and IECEx by KEMA and accordingCSA c-us and FM for use in Intrinsically Safe applications with an ambient temperature of -40°C to +70°C (-40°F to +158°F).
  • The ATEX markings for gas and dust applications are:
    ATEX Certification II 1 G Ex ia IIC T4
    ATEX Certification II 1 D Ex iaD 20 IP 65/67 T 100 °C.
  • The IECEx markings for gas and dust applications are: Ga Ex ia IIC T4 and Ex iaD 20 IP 65/67 T100 °C.
  • The CSA c-us markings are: Class I/II/III, Division 1, Groups A, B, C, D, E, F, G, Temperature class T4 and Class I, Zone 0, AEx ia IIC T4.
  • The FM markings are: Class I/II/III, Division 1, Groups A, B, C, D, E, F, G, Temperature class T4 and Class I, Zone 0, AEx ia IIC T4.

It is allowed to connect up to three I.S. power supplies to power the unit, sensor and backlight. The F016-PD-XI offers a 8.2V DC sensor supply to power e.g. a Namur sensor or the input voltage to power an analog sensor. An ATEX approved flame proof enclosure with rating ATEX Certification II 2 GD EEx d IIB T5 is available as well.

Configuration example IIA - IIB and IIC
F016-P-(OT)-PC-(PX)-XI-(ZB)- Battery powered unit

Configuration example IIA - IIB and IIC F016-P-(OT)-PC-(PX)-XI-(ZB) - Battery powered unit

* Sensor supply voltage for pulse flowmeter type P : Terminal 3: 1.2 / 3.2V DC.
Please note: type PX may be used in combination with the battery (type PC). PX will power the unit; the battery will be disabled automatically till power is disconnected.

Configuration example IIA - IIB and IIC -
F016-P-OT-PX-XI-(ZB)- Basic power supply 8 - 30V DC

Configuration example IIA - IIB and IIC - F016-P-OT-PX-XI-(ZB) - Basic power supply 8 - 30V DC

Configuration example IIA - IIB and IIC -
F016-P-OT-PX-XI-ZB- Basic power supply 8 - 30V DC

Configuration example IIA - IIB and IIC F016-P-OT-PX-XI-ZB - Basic power supply 8 - 30V DC

Configuration example IIA - IIB and IIC
F016-P-OT-PD-XI-ZB- Power supply 16 - 30V DC

Configuration example IIA - IIB and IIC F016-P-OT-PD-XI-ZB - Power supply 16 - 30V DC

Configuration example IIA - IIB and IIC
F016-A-OT-PD-XI-ZB- Power supply 16 - 30V DC

Configuration example IIA - IIB and IIC F016-A-OT-PD-XI-ZB - Power supply 16 - 30V DC

Configuration example IIA - IIB and IIC
F016-A-OT-PL-XI-ZB- Input loop powered

Configuration example IIA - IIB and IIC F016-A-OT-PL-XI-ZB - Input loop powered

Configuration example IIA - IIB and IIC
F016-A-OT-PX-XI-ZB- Basic power supply 8 - 30V DC

Configuration example IIA - IIB and IIC F016-A-OT-PX-XI-ZB - Basic power supply 8 - 30V DC


SPECIFICATIONS

Display

Type: High intensity reflective numeric and alphanumeric LCD, UV-resistant.
Dimensions: 90 x 40mm (3.5" x 1.6").
Digits: Seven 17mm (0.67") and eleven 8mm (0.31") digits. Various symbols and measuring units.
Refresh rate: User definable: 8 times/sec. - 30 secs - off.
Option ZB: Transflective LCD with bi-color LED-backlight; green / amber. Intensitiy and color selected through the keyboard. Good readings in full sunlight and darkness. Also available Intrinsically Safe.

Operating Temperature

Standard Unit: -40°C to +80°C (-40°F to +178°F).
Intrinsically Safe: -40°C to +70°C (-40°F to +158°F).

Power Requirements

Type PB: Long life Lithium battery - life-time depends upon settings and configuration - up to 5 years.
Type PC: Intrinsically Safe long life lithium battery - life-time depends upon settings and configuration - up to 5 years.
Type PD: 16 - 30V DC. Power consumption max. 1 Watt.
Type PF: 24V AC / DC ± 10%. Power consumption max. 15 Watt.
Type PL: Input loop powered from sensor signal 4 - 20mA (type A).
Type PM: 115 - 230V AC ± 10%. Power consumption max. 15 Watt.
Type PX: 8 - 30V DC. Power consumption max. 0.3 Watt.
Type ZB: 20 - 30V DC. Power consumption max. 1 Watt. With type PF / PM: internally powered.
     Note PB/PF/PM Not available Intrinsically Safe
     Note PF/PM The total consumption of the sensor, active output type OA and backlight type ZB may not exceed 400mA @ 24V DC
     Note For Intrinsically Safe applications, consult the safety values in the certificate

Sensor Excitation

Type PB/PC/PX: 3.2V DC for pulse signals and 1.2V DC for coil pick-up.>
     Note This is not a real sensor supply. Only suitable for sensors with a very low power consumption like coils (sine wave) and reed-switches.
Type PD: for pulse signals: 1.2 / 3.2 / 8.2V DC - max. 5mA@8.2V DC. For analog signals, the sensor supply voltage is according to the power supply voltage connected.
Type PF / PM: With pulse input: 1.2 / 3.2 / 8.2 / 12 / 24V DC - max. 400mA @ 24V DC. With analog input: 8.2 / 12 / 24V DC - max. 400mA @ 24V DC.

Terminal Connections

Type: Removable plug-in terminal strip. Wire max. 1.5mm2 and 2.5mm2.

Data Protection

Type: EEPROM backup of all settings. Backup of running totals every minute. Data retention at least 10 years.
Pass-code: Configuration settings can be pass-code protected.

Casing

Window: Polycarbonate window.
Sealing: Silicone.
Control Keys: Three industrial micro-switch keys. UV-resistant silicone keypad.

Aluminum Wall / Field Mount Enclosures

General: Die-cast aluminum wall/field mount enclosure IP67 / NEMA 4X with 2-component UV-resistant coating.
  Dimensions: 130 x 120 x 75mm (5.12" x 4.72" x 2.95") - W x H x D.
  Weight: 1100 grams/2.42 lbs
Type HA: Cable entry: 2 x PG9 and 1 x M20.
Type HM: Cable entry: 2 x M16 and 1 x M20.
Type HN: Cable entry: 1 x M20.
Type HO: Cable entry: 2 x M20.
Type HP: Cable entry: 6 x M12.
Type HT: Cable entry: 1 x 1/2" NPT.
Type HU: Cable entry: 3 x 1/2" NPT.
Type HV: Cable entry: 4 x M20.
Type HZ: Cable entry: no holes.

GRP Wall / Field Mount Enclosures

General: GRP wall/field mount enclosure IP67 / NEMA 4X, UV-resistant and flame retardant.
  Dimensions: 130 x 120 x 75mm (5.12" x 4.72" x 2.95") - W x H x D.
  Weight: 600 grams/1.33 lbs
Type HD: Cable entry: no holes.
Type HE: Cable entry: 2 x Ø 16mm and 1 x Ø 20mm.
Type HF: Cable entry: 1 x Ø 22mm (7/8").
Type HG: Cable entry: 2 x Ø 20mm.
Type HH: Cable entry: 6 x Ø 12mm.
Type HJ: Cable entry: 3 x Ø 22mm (7/8").
Type HK: Flat bottom, cable entry: no holes.

Panel Mount Enclosures

Dimensions: 130 x 120 x 60mm (5.12" x 4.72" x 2.36") - W x H x D.
  Panel cut-out: 115 x 98mm (4.53" x 3.86") L x H.
Type HB: Die-cast aluminum panel mount enclosure IP65 / NEMA 4.
  Weight: 600 grams/1.33 lbs
Type HC: GRP panel mount enclosure IP65 / NEMA 4, UV-resistant and flame retardant.
  Weight: 450 grams/1 lb

ABS Wall / Field Mount Enclosures

General: Silicone free ABS wall/field mount enclosure IP65 with EPDM and PE sealings. UV-resisitant polyester keypad (old HD enclosure).
  Dimensions: 130 x 114 x 71mm (5.1" x 4.5" x 2.8") - W x H x D.
  Weight: 450 grams/1 lb
Type HS: Cable entry: no holes.

Intrinsically Safe

ATEX Certification: ATEX Certification II 1 G Ex ia IIC T4. II 1 D Ex iaD 20 IP 65 / 67 T 100 °C.
IECEx Certification: Ga Ex ia IIC T4. Ex iaD 20 IP 65 / 67 T 100 °C.
CSA c-us Certification: Intrinsically Safe for Class I/II/III, Div. 1, Groups A, B, C, D, E, F, G, Temp. class T4 and Class I, Zone 0, AEx ia IIC T4.
FM certification: Intrinsically Safe for Class I/II/III, Div. 1, Groups A, B, C, D, E, F, G, Temp. class T4 and Class I, Zone 0, AEx ia IIC T4.
Ambient: -40°C to +70°C / -40° to +158°F.

Hazardous Area

Intrinsically Safe Type XI: ATEX approval ref.: ATEX Certification II 1 GD EEx ia IIB/IIC T4 T100°C. Maximum ambient +70°C (158°F).
Explosion proof Type XF: ATEX approval ref.: ATEX Certification II 2 GD EEx d IIB T5. Dimensions of enclosure: 300 x 250 x 200mm (11.8" x 9.9" x 7.9") L x H x D.
  Weight: Appr. 15kg/33 lbs

Environment

Electromagnetic compatibility: Compliant ref: EN 61326 (1997), EN 61010-1 (1993)

Signal Input

Type P: Coil / sine wave (minimum 20mVpp or 80mVpp - sensitivity selectable), NPN/PNP, open collector, reedswitch, Namur, active pulse signals 8 - 12 and 24V DC.
  Frequency: Minimum 0Hz - maximum 7kHz for total and flow rate. Maximum frequency depends on signal type and internal low-pass filter. E.g. reed switch with low-pass filter: max. frequency 120Hz.
  K-Factor: 0.000010 - 9,999,999 with variable decimal position.
  Low-pass filter: Available for all pulse signals.
  Option ZF: coil sensitivity 10mVpp.
  Option ZG: coil sensitivity 5mVpp.
Type A: (0)4 - 20mA. Analog input signal can be scaled to any desired range within 0 - 20mA.
Type U: 0 - 10V DC. Analog input signal can be scaled to any desired range within 0 - 10V DC.
  Accuracy: Resolution 16 bit. Error < 0.01mA / ± 0.05% FS. Low level cut-off programmable.
  Span: 0.001 / 999,999 with variable decimal position.
  Update time: Four times per second
  Voltage drop: Type A: max. 2V DC @ 20mA
  Voltage drop: Type A - PL (loop powered): max. 2.6V DC @ 20mA
  Load impedance: Type U: 3kΩ
  Relationship: Linear and square root calculation
     Note For signal type A and U: external power to sensor is required; e.g. type PD

Signal Output

Function: Pulse output - transmitting accumulated total.
Frequency: Max. 500Hz. Pulse length user definable between 1msec up to 10 seconds.
Type OA: One active 24V DC transistor output (PNP); load max. 400mA (requires PF or PM).
Type OR: One electro-mechanical relay output - isolated; max. switch power 230V AC (N.O.) - 0.5A (requires PF or PM).
Type OT: One passive transistor output (NPN) - not isolated. Max. 50V DC - 300mA per output.

Operational

Displayed functions:
    • Linearized flow rate and / or total.
    • Linearized total and accumulated total
    • Total can be reset to zero by pressing the CLEAR-key twice.

Total

Digits: 7 digits
Units: L, m3, GAL, USGAL, KG, lb, bbl, no unit
Decimals: 0 - 1 - 2 or 3
     Note Total can be reset to zero

Accumulated Total

Digits: 11 digits
Units / decimals: According to selection for total
     Note Cannot be reset to zero

Flow Rate

Digits: 7 digits
Units: mL, L, m3, Gallons, KG, Ton, lb, bl, cf, RND, ft3, scf, Nm3, Nl, igal - no units
Decimals: 0 - 1 - 2 or 3
Time units: /sec - /min - /hr - /day

ACCESSORIES

Mounting Accessories

FWX-ACF02: Stainless steel wall mounting kit.
FWX-ACF05: Stainless steel pipe mounting kit (worm gear clamps not included).
FWX-ACF06: Two stainless steel worm gear clamps Ø 44 - 56mm.
FWX-ACF07: Two stainless steel worm gear clamps Ø 58 - 75mm.
FWX-ACF08: Two stainless steel worm gear clamps Ø 77 - 95mm.
FWX-ACF09: Two stainless steel worm gear clamps Ø 106 - 138mm.
FWX-ACF10: Customized Grevopal tag plates for ACF02 and ACF05, including stainless steel screws. Dimension: 95mm x 12.5mm (3.75” x 0.50”).

ORDERING INFORMATION

Standard Model Number Configuration (example): F016-P-HC-OT-PX-XX-ZX

To aid in the construction of a Fluidwell model number a model configurator must be used. The path to this Configurator is contained in the link shown below. However, it would help to first review the options shown below.

NOTE: If you require the product to be Intrinsically Safe (ATEX, IECEx, CSA c-us or FM.), the options you choose should only include those options that carry the ATEX symbol next to them. The Configurator will not allow you to mix and match options, unless the product is to be used in a Safe Area.

Once a new model is generated using the Configurator, you will
  1. see the price of the fully configured model
  2. have an opportunity to purchase the product
  3. have the capability to e-mail the configuration to us, yourself, or a third person

To launch the configurator, click here

Sensor Input Signal

A ATEX Certification (0)4 - 20mA input
P ATEX Certification Pulse input: coil, npn, pnp, namur, reed-switch
U ATEX Certification 0 - 10V DC input

Panel Mount Enclosures - IP65 / NEMA 4

HB ATEX Certification Aluminum enclosure
HC ATEX Certification GRP enclosure

GRP Field / Wall Mount Enclosures - IP67 / NEMA 4X

HD ATEX Certification Cable entry: no holes
HE ATEX Certification Cable entry: 2 x Ø 16mm & 1 x Ø 20mm
HF ATEX Certification Cable entry: 1 x Ø 22mm (7/8")
HG ATEX Certification Cable entry: 2 x Ø 20mm
HH ATEX Certification Cable entry: 6 x Ø 12mm
HJ ATEX Certification Cable entry: 3 x Ø 22mm (7/8")
HK ATEX Certification Flat bottom, cable entry: no holes

Aluminum Field / Wall Mount Enclosures - IP67 / NEMA 4X

HA ATEX Certification Cable entry: 2 x PG9 + 1 x M20
HM ATEX Certification Cable entry: 2 x M16 + 1 x M20
HN ATEX Certification Cable entry: 1 x M20
HO ATEX Certification Cable entry: 2 x M20
HP ATEX Certification Cable entry: 6 x M12
HT ATEX Certification Cable entry: 1 x 1/2" NPT
HU ATEX Certification Cable entry: 3 x 1/2" NPT
HV ATEX Certification Cable entry: 4 x M20
HZ ATEX Certification Cable entry: no holes

ABS Field / Wall Mount Enclosures

HS ATEX Certification Silicone free ABS field enclosure IP65 – Cable entry: no holes (old HD enclosure)

Output

OA   One active transistor output - requires PF or PM
OR   One mechanical relay output - requires PF or PM
OT ATEX Certification One passive transistor output - standard configuration

Power Supply

PB   Lithium battery powered
PC ATEX Certification Lithium battery powered - Intrinsically Safe
PD ATEX Certification 16 - 30V DC + sensor supply
PF   24V AC / DC + sensor supply
PL ATEX Certification Input loop powered from sensor signal 4 - 20mA (type A)
PM   115 - 230V AC + sensor supply
PX ATEX Certification Basic power supply 8 - 30V DC (no real sensor supply)

Hazardous Area

XI ATEX Certification Intrinsically Safe
XF   EExd enclosure - 3 keys
XX   Safe area only

Other Options

ZB ATEX Certification Backlight
ZF ATEX Certification Coil input 10mVpp
ZG ATEX Certification Coil input 5mVpp
ZX ATEX Certification No options

The bold marked text contains the standard configuration.

DOCUMENTATION

The documentation can be downloaded from these links:
F016: Data Sheet
Request an Instruction Manual
Low-Cost Explosion Proof Enclosure
Fluidwell Information
Fluidwell Intrinsically Safe data for FM, CSA, and ATEX

See How You can Use Precision Digital Products for